Carried out an EICR and am now doing the remedials.
Poor IR results on conservatory ring which I have now identified as the electric UFH.
The UFH has 2 x line and 2 x neutral conductors on the load side of control panel (same terminal). I'm not sure why as the conservatory is only 4m x 3m so not sure why it needed two separate feeds.
Both cables of the UFH show faults. Side 1 N-E 0.24Mohms, side 2 N-E 0.75Mohms.
There is no earth conductor going to the mat/cable (whatever it is), just 2 x line and 2 x neutral plus the 2 core cable for the floor thermostat.
I have disconnected, but I was wondering if there is absolutely anything you can do to remedy this? I'm guessing moisture has got into the conservatory floor, and there is nothing you can do about it, but thought I'd ask.
Cheers all.
Poor IR results on conservatory ring which I have now identified as the electric UFH.
The UFH has 2 x line and 2 x neutral conductors on the load side of control panel (same terminal). I'm not sure why as the conservatory is only 4m x 3m so not sure why it needed two separate feeds.
Both cables of the UFH show faults. Side 1 N-E 0.24Mohms, side 2 N-E 0.75Mohms.
There is no earth conductor going to the mat/cable (whatever it is), just 2 x line and 2 x neutral plus the 2 core cable for the floor thermostat.
I have disconnected, but I was wondering if there is absolutely anything you can do to remedy this? I'm guessing moisture has got into the conservatory floor, and there is nothing you can do about it, but thought I'd ask.
Cheers all.