Did an EICR on a small office unit. TT system, and Ze of stake was >800 ohms.

Zs of DB was just 8 ohms, which I suspect is due to the structural steelwork.

If I did this installation I would have used the steelwork as the 'stake', in which case I'm inclined to forgo the bad Ze of the stake and say the Ze of the steelwork is enough!

Any comments?
 
Structural steel has to be embedded in the foundations to be used as an electrode.....might be difficult to ensure it meets the requirements if it's existing and not inspected while being built. Might also be difficult on an existing system to verify an Ra reading off steel is genuine and not affected by parallel paths. Unless there was an initial verification cert available I would not rely on steel as an electrode on an existing install.
 
Did an EICR on a small office unit. TT system, and Ze of stake was >800 ohms.

Zs of DB was just 8 ohms, which I suspect is due to the structural steelwork.

If I did this installation I would have used the steelwork as the 'stake', in which case I'm inclined to forgo the bad Ze of the stake and say the Ze of the steelwork is enough!

Any comments?

8 ohms!!! Get that down below 1, or Eng will have your guts for garters!!!
:)
 
Yeah, Eng isn't gonna like that Ra reading ;)

I agree the problem with the 8ohm steelwork reading is you don't know how much contribution parallel paths are making therefore you don't know what you'll be left with if the plumber/gasman etc replaces his copper main with plastic.

You could try extending the existing rod with another 2.3m rod on top of it, if the existing rod is one of those 1 meter specials that seem quite popular then the Ra should drop dramatically for relatively little work and cost.
 

Reply to Poor Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
610
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top