cliffed

-
Arms
Joined
Dec 20, 2009
Messages
2,183
Reaction score
697
Location
Worcester
jus done a new supply to a portcabin,quite a big site main supply 400 amps 3p,came of local db,wiv 3core swa 16mm backed by 63 amp mcb.Installed tt system,done all checks a ok,Ze .26 ohms,very low for tt,but well expected because of site conditions.Went back there recently & on way home thinkin bout the job,an air conditioning unit had been added to the cabin,wiv cable tray from main building attached to cabin, this being fixed to the main steel sructure of the building brings the main earthing system into the cabin i originally had tt.Will main bonding criteria now need 2 be implemented, like 2 no your thinkin on this thxs.
 
You should main bond the incoming AC lines to your portacabin MET if they are introducing an earth potential....is the main earthing system TNS or TNCS?....bit of a grey area with portacabins as TNCS is permitted for a fixed building of a construction site,but prohibitted for caravans or 'similar contructions'......Possibly if TNCS you should insulate the tray from the earthing system of your portacabin.
Not wanting to start another Ra debate but a TT Ze of 0.26 ohms seems unrealistic....are you sure there are no parallel paths back to the main earthing system when you measured?
 
THe site is a big recyling plant area,deep in a quarry wiv various equipment,earhing rods everywhere,making it a very low resistance for earth,the main supply is tncs, tt =.26 zs at db=.26 also . May have 2 insulate tray offa building,but this was installed by others,& a odd chance that i revisited the site & spotted it.
 

Reply to portacabin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top