jus done a new supply to a portcabin,quite a big site main supply 400 amps 3p,came of local db,wiv 3core swa 16mm backed by 63 amp mcb.Installed tt system,done all checks a ok,Ze .26 ohms,very low for tt,but well expected because of site conditions.Went back there recently & on way home thinkin bout the job,an air conditioning unit had been added to the cabin,wiv cable tray from main building attached to cabin, this being fixed to the main steel sructure of the building brings the main earthing system into the cabin i originally had tt.Will main bonding criteria now need 2 be implemented, like 2 no your thinkin on this thxs.