StopTapBob

I have fitted an RCD fused spur to that covers the bathroom lights.
The spur is fitted at the top of the wall outside the bathroom touching the ceiling.
The customer is complaining that the fused spur should be accessible. In my opinion it is.
I have looked through the regs and can find nothing that says that they should be at a certain height.
Any comments would be appreciated.
 
BS 7671 does not give specific heights for accessories.

The Building Regulations require the following :

Accessories must be mounted between 450mm and 1200mm from the finished floor level in habitable rooms in new dwellings.
 
Hi Sintra


Yes that is the only thing I could think of too. Part M, but its an old property so I am presuming that does not cover this installation?

Thanks
 
All electrical equipment must be accessible for operation, inspection & testing, maintenance and repair. 132.12

Is this fcu accessible for operation as you have mentioned it is at ceiling height?
 
Yes it is accessible. Its at ceiling height so does require step ladders to reach it. But I still consider that to be accessible. What do you think?
 
You have answered the question yourself. As designer of the circuit you have stated that it is accessible so you are complying with the regs.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Postion of RCD fused Spur
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
StopTapBob,
Last reply from
StopTapBob,
Replies
10
Views
5,877

Advert

Back
Top