Hi was wondering if anyone could help or knew someone who could help us.
The programmer has gone kaput in our potterton 2 ultra 2 dv programmer boiler
We can not get hold of a replacement :(
Does anyone know of anyone capable of ( if it is possible to do so ) fitting a generic programmer or mechanical switching in newton abbot.
Otherwise the local plumbers said it is new boiler time for us.
Cheers:smiley2:
 
Hi was wondering if anyone could help or knew someone who could help us.
The programmer has gone kaput in our potterton 2 ultra 2 dv programmer boiler
We can not get hold of a replacement :(
Does anyone know of anyone capable of ( if it is possible to do so ) fitting a generic programmer or mechanical switching in newton abbot.
Otherwise the local plumbers said it is new boiler time for us.
Cheers:smiley2:



"Hello magletti",

It is definitely NOT correct that you will need a New Boiler just because the Internal / Built in Programmer has failed in your Potterton Ultra 2 Boiler !


Although I am not an Electrician - I am a Heating Engineer - I can tell You categorically that almost ANY External Programmer[2 Channel] can be installed / wired up to your Potterton Ultra 2 System Boiler.

The Wiring Diagrams are in the Boiler Installation Instructions - If You don`t have these here is a Link to where You can download a PDF Copy:

http://www.acwilgar.co.uk/Boiler-Manual-PDF/Potterton/POTTERTON ULTRA 2 30,40,50,60,80 .pdf

If You - Or your `Plumber`/ Heating Engineer finds the Electrical section You will see the details for Wiring the Boiler with an EXTERNAL Programmer - i.e: one that is NOT fitted into the Boiler.

There are many Manufacturers of these - I favour Honeywell Controls but there are also Danfoss - Drayton and many others.

However - After the `Diagnosis` / `Technical Opinion` from your `Plumbers` - When You find the wiring details I think that you would be better off getting a Professional Electrician to rewire your Potterton Ultra 2 Boiler to the New External Programmer.


I hope that this is helpful to You - it will probably be a couple of Thousand of Pounds cheaper than installing a New Boiler !


Regards,


Chris - Heating Engineer - Gas Engineer - Plumber / Heating, Plumbing and Gas Contractor
 
Last edited:
"Hello magletti",

It is definitely NOT correct that you will need a New Boiler just because the Internal / Built in Programmer has failed in your Potterton Ultra 2 Boiler !


Although I am not an Electrician - I am a Heating Engineer - I can tell You categorically that almost ANY External Programmer[2 Channel] can be installed / wired up to your Potterton Ultra 2 System Boiler.

The Wiring Diagrams are in the Boiler Installation Instructions - If You don`t have these here is a Link to where You can download a PDF Copy:

http://www.acwilgar.co.uk/Boiler-Manual-PDF/Potterton/POTTERTON ULTRA 2 30,40,50,60,80 .pdf

If You - Or your `Plumber`/ Heating Engineer finds the Electrical section You will see the details for Wiring the Boiler with an EXTERNAL Programmer - i.e: one that is NOT fitted into the Boiler.

There are many Manufacturers of these - I favour Honeywell Controls but there are also Danfoss - Drayton and many others.

However - After the `Diagnosis` / `Technical Opinion` from your `Plumbers` - When You find the wiring details I think that you would be better off getting a Professional Electrician to rewire your Potterton Ultra 2 Boiler to the New External Programmer.


I hope that this is helpful to You - it will probably be a couple of Thousand of Pounds cheaper than installing a New Boiler !


Regards,


Chris - Heating Engineer - Gas Engineer - Plumber / Heating, Plumbing and Gas Contractor


Many thanks for all your help I will be looking into this asap!!!
 
Many thanks for all your help I will be looking into this asap!!!



"Hello again magletti",

Please let Me know with a Post on here how You get on - I hate the idea that someone would tell you that a New Boiler is required just because you cannot get another `Built in` / Internal Programmer for the Potterton Ultra 2 Boiler.


Obviously I am stating this from the view that the internal programmer which has `Failed` is the ONLY problem with the Boiler - ?


I have NOT researched the fact that these Internal Programmer cannot be obtained - I take it that You will have looked around.

I hope that My noticing your Post will have resulted in You NOT being convinced to have a New Boiler installed as this is definitely NOT required just because of the Programmer.


Regards,


Chris - Heating Engineer
 
Cheers Chris

I fix computers and you get a similar thing with them unfortunately. Unnecessary software sold for un-related problems, all to eager to get you to buy a new computer for a faulty component.

We were under the impression the programmer was akin to the motherboard in a PC and the boiler would not function without it.

I am glad you enlightened us!

I think it is a universal trait that there is money to be made where there is a lack of knowledge!!

Many thanks again and will post up the result of your help
 
Cheers Chris

I fix computers and you get a similar thing with them unfortunately. Unnecessary software sold for un-related problems, all to eager to get you to buy a new computer for a faulty component.

We were under the impression the programmer was akin to the motherboard in a PC and the boiler would not function without it.

I am glad you enlightened us!

I think it is a universal trait that there is money to be made where there is a lack of knowledge!!

Many thanks again and will post up the result of your help



"Hello again magletti",


I have heard quite a lot about people recommending unnecessary Software etc. for Computers and although that can obviously be quite costly - NOT as `Costly` as a NEW Boiler - what You were told about probably needing a NEW Boiler is basically FRAUD !

I can see how you could be convinced that an Integral Component / the Built in Programmer NOT being available [have You checked this ?] would render the Boiler irreparable - especially when told this by your `Plumbers`.

This could have been a VERY Expensive piece of BAD Advice !

I am fairly sure that those `Plumbers` would have tried to charge You at least £2000.00 to replace your Boiler !

Good luck in getting a Professional Electrician to install an External Programmer and wire it to your Potterton Ultra 2 Boiler.

I look forward to reading that this has been done and that your Boiler / Heating & Hot Water System is working again.


Regards,

Chris - Heating Engineer
 
"Hello again magletti",


I have heard quite a lot about people recommending unnecessary Software etc. for Computers and although that can obviously be quite costly - NOT as `Costly` as a NEW Boiler - what You were told about probably needing a NEW Boiler is basically FRAUD !

I can see how you could be convinced that an Integral Component / the Built in Programmer NOT being available [have You checked this ?] would render the Boiler irreparable - especially when told this by your `Plumbers`.

This could have been a VERY Expensive piece of BAD Advice !

I am fairly sure that those `Plumbers` would have tried to charge You at least £2000.00 to replace your Boiler !

Good luck in getting a Professional Electrician to install an External Programmer and wire it to your Potterton Ultra 2 Boiler.

I look forward to reading that this has been done and that your Boiler / Heating & Hot Water System is working again.


Regards,

Chris - Heating Engineer



"Hello again magletti",


Please don`t be offended by this - just in case My explanations about the `External Programmer` were not detailed enough:

When I state `External Programmer` - can I take it that You know I mean an Electronic Programmer that will be fitted to a Wall or other suitable location near the Boiler and has to be wired to the Boiler - not a Programmer that can take the place of the existing Internal / Integral Programmer that is fitted into the Boiler.

The existing `Built - in` Programmer wiring would be unplugged from its `Plug - in` connections within the Boiler - the wires should be Cut Off to prevent future confusion - and for appearence purposes you will probably need to just leave the Programmer in place on the Boiler - unless You have the `Blanking Plate` that was taken Off in order to Fit the Programmer - ?


If this was obvious to You then I hope that the above will help another Reader of this information in the future.


Regards,


Chris
 
"Hello magletti",

It is definitely NOT correct that you will need a New Boiler just because the Internal / Built in Programmer has failed in your Potterton Ultra 2 Boiler !


Although I am not an Electrician - I am a Heating Engineer - I can tell You categorically that almost ANY External Programmer[2 Channel] can be installed / wired up to your Potterton Ultra 2 System Boiler.

The Wiring Diagrams are in the Boiler Installation Instructions - If You don`t have these here is a Link to where You can download a PDF Copy:

http://www.acwilgar.co.uk/Boiler-Manual-PDF/Potterton/POTTERTON ULTRA 2 30,40,50,60,80 .pdf

If You - Or your `Plumber`/ Heating Engineer finds the Electrical section You will see the details for Wiring the Boiler with an EXTERNAL Programmer - i.e: one that is NOT fitted into the Boiler.

There are many Manufacturers of these - I favour Honeywell Controls but there are also Danfoss - Drayton and many others.

However - After the `Diagnosis` / `Technical Opinion` from your `Plumbers` - When You find the wiring details I think that you would be better off getting a Professional Electrician to rewire your Potterton Ultra 2 Boiler to the New External Programmer.


I hope that this is helpful to You - it will probably be a couple of Thousand of Pounds cheaper than installing a New Boiler !


Regards,


Chris - Heating Engineer - Gas Engineer - Plumber / Heating, Plumbing and Gas Contractor



"Hello magletti",


I was hoping that You would have let Us / Me know the outcome of your Boiler / External Programmer required problem.

Could You please post an Update on here - Just to let Me know whether My advice helped You or not.

I hope that You managed to arrange for a Professional Electrician to install an External Programmer as I suggested and that solved your `Boiler needs to be replaced` [!] problem - ?

We encourage people to please update the Forum when they have been given `Good Advice` - especially in case such as Yours - where I believe that My Advice about you NOT requiring a New Boiler will have saved you perhaps £2000.00 with a Heating Engineer - or much more with one of the Larger Boiler Installation Companies.



Regards,

Chris
 
"Hello magletti",


I was hoping that You would have let Us / Me know the outcome of your Boiler / External Programmer required problem.

Could You please post an Update on here - Just to let Me know whether My advice helped You or not.

I hope that You managed to arrange for a Professional Electrician to install an External Programmer as I suggested and that solved your `Boiler needs to be replaced` [!] problem - ?

We encourage people to please update the Forum when they have been given `Good Advice` - especially in case such as Yours - where I believe that My Advice about you NOT requiring a New Boiler will have saved you perhaps £2000.00 with a Heating Engineer - or much more with one of the Larger Boiler Installation Companies.



Regards,

Chris


"Hello magletti",


Could You please let Me / Us know what happened regarding You having an External Programmer installed on your Heating System / Boiler.

I am disappointed that you have not replied to my other request for an Update.


As You will have received `reminder Emails` from the Forum when I have written a message to You on this thread - because you posted your original question on here - I am a bit surprised that You have not replied.


My original answer to You could have been the reason why you saved at least £2000 - by NOT having a New Boiler etc. installed - I would have thought that merited an `Update` on here from You - ?


Please don`t be offended by this - I am just wondering how You got on regarding getting your Heating and Hot Water working again.


Regards,


Chris
 

Reply to potterton 2 ultra 2 dv programer in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

Heh I know the brochures for courses with stock images of women using tools in random scenarios but when you're there it never happens, it's all...
    • Like
Replies
2
Views
357
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top