Need to supply a power shower. Consumer unit - Rewirable fuses. No RCD

No equipotential bonding in bathroom

Main bonding 6 mm - maximum

Can I supply it via one of the circuits throught an RCD and upgrade bonding. Was thinking of lighting circuit upstairs which will also cover no bonding in bathroom (tiles all over including floor) so cannot run bonding to metal as it will look awful. Shower pump rated at 3 amp.

Any suggestion. Owner cannot afford new consumer unit.

Thanks.
 
If you have no alternative then spuring off the lighting circuit is OK but not the best practice.
Use an RCD fused spur to supply the shower pump and fit a 3a fuse. I assume that the pump is in the loft, if so then you need a MWC, and i dont think it is notifiable either if that is the case. But i may yet stand corrected, however if it is in the bathroom then it is notifiable.

Dont worry about existing CU and bonding etc as long as the circuit you work on is in spec and the gas and water bonds are OK from incomming services to CU earth connection just make a note on your paperwork that it conforms to whatever edition regs and customer declines offer to upgrade. There is no longer the requirement to bond all bits of metal anymore. It could be compliant anyway if the tails are 16mm, main earth 10mm then supplementary at 6mm is OK, assuming 80a or smaller cut out fuse.


Cheers..........Howard
 
Last edited by a moderator:
Shower pump will be fitted in airing cupboard in corridor upstairs. Will use a spur with RCD in circuit ring circuit.

Main bongind are 6mm all of the wires seems to be that size.

I know that I have to bring all the main bonding to 16 and 10 mm to comply with regulation. There is already a shower connected properly via surrey flange. It just need a pump in it a there is no pressure at all.

However if the lighting circuit in the bathroom is not on RCD, the pipes in the bathroom will have to be bonded together. Is there another alternative to that.

Sirkit Brk - what is a MWC.

Cheers
 

Reply to Power shower supply in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
590
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top