Hi,

Just been looking into powerline adaptors and just wondering how they work. I read that they operate on far higher frequencies to mains power, but if that's the case why don't you have to separate band 1 and 2 like in other applications?

Just hoping to find out the reasons

Cheers Lads
 
There are two aspects to separating the different bands of cables. One is to prevent mains voltages from getting into telecomms / data circuits in the event of damage; this can be overridden if the data cables are insulated sufficiently for the highest voltage present. E.g. although a bell circuit might use 12V itself, if it is wired in a mains-rated cable there's another layer of adequate insulation between its conductors and the mains conductors and they can run together. Obviously this aspect doesn't apply to the powerline data adaptor because it doesn't have a cable of its own.

The second aspect is preventing interference. Data and comms interfaces are designed to be as resistant to incoming interference as possible, so that fields surrounding the cables don't disrupt the signal. But, where power and data run very close together, the field strengths can be high and some interference is likely. However, the signal encoding and modulation system used in the powerline adaptor is designed to work in an extremely electrically noisy environment, not just being near to mains cables but actually superimposed on the mains. So, it doesn't benefit from segregation because there's nothing worse to segregate it from.

They are a fudge, and will never offer the data performance of a dedicated data link. They do the best they can with the available connectivity, by sacrificing performance for interference-proofing.
 
There are two aspects to separating the different bands of cables. One is to prevent mains voltages from getting into telecomms / data circuits in the event of damage; this can be overridden if the data cables are insulated sufficiently for the highest voltage present. E.g. although a bell circuit might use 12V itself, if it is wired in a mains-rated cable there's another layer of adequate insulation between its conductors and the mains conductors and they can run together. Obviously this aspect doesn't apply to the powerline data adaptor because it doesn't have a cable of its own.

The second aspect is preventing interference. Data and comms interfaces are designed to be as resistant to incoming interference as possible, so that fields surrounding the cables don't disrupt the signal. But, where power and data run very close together, the field strengths can be high and some interference is likely. However, the signal encoding and modulation system used in the powerline adaptor is designed to work in an extremely electrically noisy environment, not just being near to mains cables but actually superimposed on the mains. So, it doesn't benefit from segregation because there's nothing worse to segregate it from.

They are a fudge, and will never offer the data performance of a dedicated data link. They do the best they can with the available connectivity, by sacrificing performance for interference-proofing.
Cheers man, knew there had to be a catch!
 
I have used them in the past when absolutely no other solution.
generaly if they do work then 5 to 10% of the quoted speed seems normal.
 

Reply to Powerline Adaptor and power bands in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

  • Question
Ah OK, that makes sense. Thank you Avo.
Replies
12
Views
2K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top