6 Econ 7 storage heaters in an old local authority flat. Each heater supplied from its own individual 20A MCB in a Wylex fuse board. 4 of the heaters work. 2 have suddenly stopped working as there is no 230v supply to these heaters.
Checked at the board and each MCB has a 230v supply? Econ 7 supply OK and working between 0200-0700
There is an Enbray contactor fitted to the system. This is not something I've come across before and could it be fitted 'downstream' of the MCBs?
Could this be the issue and, if so, is this the DNOs equipment?
If there is 230v at the source and not and the heater then there is something in the middle causing a problem, you could find the contactor has failed on a couple of poles, not uncommon. I changed one some time back where it had failed on one pole.
Failing that, if you have tested each circuit and it is ok with no problems, I have no idea other than to say the heater is broken.
All the heaters work fine. Its the supply to the heaters which is the issue. I'm scratching my head as to why I have 230V at the MCB but not at the heater. Could be a break in the cable, but the circuit is a simple radial to the heater wall switch. I do mainly domestic work, so its rare for me to come across contactors and I'm wary if this is DNO equipment!
I did go to the flat at night! 5am this morning as its just next door on my way to work. What a bunch of cynics!
Never expected the contactors to be in circuit downstream of the MCB. Not something I've come across before in a domestic. I guess I expected the contactor to be energising the Econ 7 board. Sticking my head above the parapet why is it done this way? All the other E7 I've done have been fuse board fed direct off the tele switch tails.
I shall go back during the day and do some R1+R2's back to the contactor and the board!!
Matey.... you have to admit that you didn't confirm "how" you knew it was live and most of us were working on the fact that you were probably tucked up in bed !!:smile5:
Oh and by the way, I would be doing Rn + R2's too!
Reply to Problem Econ 7 in the UK Electrical Forum area at ElectriciansForums.net
  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...