R
Roger
Advice please
Ok I have RCD protected ring main on a 32 amp MCB repeating tripping so first of all established no continuity on CPC repaired that easy to find with wander lead.Thought I had found the issue as well as the conductor had broken and was touching the live.Well it looked like that when I pulled the socket off.
Reconnect at CU and still tripping.Split ring and figure out what's on it and route it takes.Started doing IR tests on splits and found 1.05Mohms between live and CPC.NE and LN fine,full range.
I then took off every socket fascia and found 2 with the earth mechanism broken.Carried on doing IR tests on all split legs and now have 2 legs with poor readings always between live and CPC.One leg between a socket and another leg from last socket in ring to CU.This now kills 3 sockets !
Its a lovely finished house ,fully tiled floor ,fitted kitchen with marble everywhere,start pulling this lot out will be a nightmare and not practical.
Why would this happen all of a sudden ?
I can get a majority of the sockets to work but its a 20amp Radial now !
Brain is frazzled,too much work and not enough time.
Ok I have RCD protected ring main on a 32 amp MCB repeating tripping so first of all established no continuity on CPC repaired that easy to find with wander lead.Thought I had found the issue as well as the conductor had broken and was touching the live.Well it looked like that when I pulled the socket off.
Reconnect at CU and still tripping.Split ring and figure out what's on it and route it takes.Started doing IR tests on splits and found 1.05Mohms between live and CPC.NE and LN fine,full range.
I then took off every socket fascia and found 2 with the earth mechanism broken.Carried on doing IR tests on all split legs and now have 2 legs with poor readings always between live and CPC.One leg between a socket and another leg from last socket in ring to CU.This now kills 3 sockets !
Its a lovely finished house ,fully tiled floor ,fitted kitchen with marble everywhere,start pulling this lot out will be a nightmare and not practical.
Why would this happen all of a sudden ?
I can get a majority of the sockets to work but its a 20amp Radial now !
Brain is frazzled,too much work and not enough time.