Hi, I've been testing my house and few others in the area as a way of gaining experience.
I'm mostly getting satisfactory results expect for insulation resistance testing on the ring circuits. I follow procedure and remove all plugs from sockets and turn them on but when I do the test I get a zero reading both on live/neutral and live/earth.
This problem is appearing in several houses not just mine so I'm obviously missing something, probably 'bleedin obvious', and I'll kick myself.
Any ideas?
Regards, Kevin
 
What happens if you open the main switch, leave all MCB's on and fuses in place and test to protective earth with line and neutral connected together?
 
Hi, thanks, quick answer, not quite sure what your suggesting here, are we talking about establishing some continuity or putting a voltage through to see what happens?
 
Just wanted to make sure that you had opened the main switch before testing. Test method 2 from GN3 is always the best way to test on periodics...
 
Sounds like there is still a load connected somewhere which would explain the L-N, and have you disconnected the neutrals at the DB as if not you would get a L-E reading through a connected load and the still connected neutrals.
 
Mmmm... yes, I think you're both on the right track. I'm using test method 1 and I suspect there is a load somewhere that is giving me the zero reading. I've read up again on GN 3 method 2 and will give that a go tomorrow.
Regards and thanks for the input to all. Kevin
 
its probably something still plugged in ( get out before its too late) it could be a washer, dryer, integrated appliance, cooker hood, whatever. In most houses there is a 6ft cabinet with tv, dvd, wii, ps3, cd player, mp3, etc which weighs 10 tonne and cannot be moved!!
 
Hi, thanks, I'm pretty sure that it's something to do with the heating setup in the houses I'm testing in, as I've definitely removed everything from all the sockets and outlets that I can find including all the spurs.
Regards, Kevin
 

Reply to Problem with IR test result on RFC's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
  • Question
I've discussed this with the OP directly as we are friends, but for anyone searching in the future, the service manual suggests that this...
Replies
2
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top