collin1443

Hi there,

I have a ----y problem as follows:

I have a ABB disconnect switch Fused at 60A, supplying 3 phase 575V(North America) to a Power Cabinet.

The Power Cabinet has several motors and a 6000VA transformer, that steps down the voltage to 230VAC/120VAC single phase.

The Cabinet also powers another Cabinet, a 15A Control Cabinet at 120VAC

Twice now, the fuses on the Power Cabinet have blown on the primary side of the transformer, and 2 VFD's
when the ABB disconnect is either being closed or opened.(We turn the disconnect off at night, and turn it on in the morning. It has only happened 2x but we have closed the disconnect probably 30-40X already.

The Transformer is fused as 6000/575V = 12A Time Delay

The 2 Motor VFD's are both 2A, and are Fused at 3.5A

What could be causing the Fuses to blow? is the transformer surging the 3 phase line?

The whole 3phase line seems to be surging, since the transformer, and the 2 motor VFD's are
the only device drawing current in the Cabinet.

Any suggestions to debug this issue?
Collin
 
As mentioned above transformers have a high inrush current and you may need to consult fuse manufacturers for correct type needed, but also consider the switchfuse itself if its old and the make and breaks is sluggish this will spike your suppy or if their is delay between the different phases making and breaking when you switch it on or off, the difference may only be a fraction of a second in some cases to cause problems.
 

Reply to Problem with Power Cabinet blowing fuses in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top