coatesykid

TNS earthing arrangement. tested ZE 0.18 ohms tested ring final circuit R1+R2 = 0.35 ohms so that makes the calculated ZS for the ring 0.53 ohms, but when I test the zs with my 1 month old fluke multi the reading comes out at 7.4 ohms can anyone tell me why this is the case
 
Have you reconnected your main earth after checking your Ze (maybe all you're seeing is any parallel paths when Zs testing your circuit).
 
Last edited:
got my r1 r2 by cross linking in cu and testing at sockets, P-P 0.3 ohms E-E 0.4 ohms aprox yes reconnect main earth
 
Last edited by a moderator:
also first time i tested it was the same and they was a fault on the circuit so I re-wired the whole ring and put new socket fronts on
 
all sockets do u think the tester could be faulty

no because you got a low Ze reading. Trusting that you reconnected the earth at the DB, it sounds like further investigation is required. I would test your meter on another circuit, like cooker, and a lighting circuit, and see what readings you are getting there. Better still test in your home.
 
how could reading be high on just 1 socket when all the sockets was less than 0.4 ohms r1 r2 test and the main earth is 0.18 ohms wouldn't that mean no mater the socket tested the zs reading should be no more than 1 ohm
 
one socket could have been spured off, with a loose connection, also your earths could be twisted together thus giving a good continuity, but have come away from the socket terminal
 

Reply to Problem with zs test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top