J

John5252

Hi all, just wondering if anyone with a lot of experience had any thoughts on this;
I've seen on farms that are usually tt earthed the mains come in and through an s type time delay rcd and then sub mains go to different buildings which are protected by standard 30ma rcds. Sometimes faults in individual buildings will only trip the individual rcd but sometimes the main rcd will trip, losing power to all buildings.
would providing an earth spike for each individual building rather than just relying on one back at the mains improve things?
or is it just one of those things and using an s type rcd is all that can be done?
cheers
 
As above, lower Ze wont make a difference, have you tested the time delayed RCD? cos if its faulty and not holding, you have whats described above 2No RCDs of same value and who knows which will disconnect first
 
Assuming you are talking about the time delayed RCDs being 100mA or higher then the only reason a time delayed RCD would trip before a non time delayed RCD is because of a faulty RCD or a simultaneous double fault.
There is the possibility of a time delayed RCD tripping as well as a single pole 30mA rcd and this would be on a neutral earth fault. To overcome this then you would need to use double pole RCDs.
Using multiple earthing systems across an installation would require careful though and planning but would not prevent the above scenarios. Because an RCD will trip on a Line Neutral imbalance, if the installation has a common supply, irrespective of the means of earthing, then any Line Neutral imbalance will be seen at all points in the installation upstream of the RCD.
 
well you should be getting discrimination between the 30mA and the 100mA s type..in favour of the s type..(thats the whole point of em)...

go get a leakage clamp on the origin...see how much leakage that s type is being subjected to...
 
Last edited by a moderator:

Reply to Problems with more than one rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
928
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top