I plan to upgrade my portable generator to a larger 40 amp max output unit.

When I originally ran the cable to my electrical panel I used 8/3 NM-B W/G wire to allow for a future upgrade.

My question is what gauge SOOW should I use for the 10 foot generator lead, 8/4 or 6/4? I'm a little confused as to why 8/3 NM-B is rated for 40 amps and 8/4 SOOW is rated for 30 amps?

Any information would be appreciated.

Thanks to all
 
Different types of cables have different current ratings for the same size conductor because the different types of insulation can handle different temperatures.
The conductors warm up during use and current ratings, when you get down to basics, are just telling you how much current a cable can carry before it gets too hot.

Some cables such as flexible cables will have lower current ratings because they are expected to be touched/handled whilst in use and so the surface temperature needs to be lower.
 
I plan to upgrade my portable generator to a larger 40 amp max output unit.

When I originally ran the cable to my electrical panel I used 8/3 NM-B W/G wire to allow for a future upgrade.

My question is what gauge SOOW should I use for the 10 foot generator lead, 8/4 or 6/4? I'm a little confused as to why 8/3 NM-B is rated for 40 amps and 8/4 SOOW is rated for 30 amps?

Any information would be appreciated.

Thanks to all
Wm welcome to the forum and why are You using SOOW wire, you can get 8/3 with ground Romex. Its good for 50 amps and it’s approved for underground and wet locations. You can go to Lowe’s or Home Depot and purchase it by the foot. Are you saying that you are going to change the 30 amp plug on the generator to a 40 amp plug. What’s the wattage of your generator ? Romex is NMS cable and who told you it’s just good for 40 amps ?
 
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?
 
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?
WM just buy the # 6 then you will for sure be OK. I don’t care what they’re website tells you if you had a copy of the 2020 NEC code book it has and article just for cables, cords and their amperages. Good luck
[automerge]1581210123[/automerge]
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?

I personally would not use SOOW cord but it’s your choice. I’m trying to help but you seem to have it figured out
 
WM just buy the # 6 then you will for sure be OK. I don’t care what they’re website tells you if you had a copy of the 2020 NEC code book it has and article just for cables, cords and their amperages. Good luck
[automerge]1581210123[/automerge]


I personally would not use SOOW cord but it’s your choice. I’m trying to help but you seem to have it figured out
I'm curious as to why you would not use SOOW?
 
I'm curious as to why you would not use SOOW?
I'm curious as to why you would not use SOOW?
The biggest reason is the amperage of # 6 is just good for 45 amps and the thickness of SOOW but it is for use in damp or wet locations. I’m just not a big fan of that type of cord. No problem and you can use it and it’s legal.
 

Reply to Proper SOOW wire gauge in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top