Prospective Fault Current | Page 2 | on ElectriciansForums

Discuss Prospective Fault Current in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It's all very well quoting guidance note 3, care to explain how you'd do it?:)

Whilst proving you have a reliable earth coming into the property which hasn't been supplemented by a gas, water or any other extraneous conductive part which has been bonded to the main earthing terminal.
 
Highest PFC will be voltage divided by Ze, but isn't it the lowest PFC that you are actually interested in - to to know if the minimum disconnection times for the protective device are met. If this is the case, do you not want voltage divided by Zs (taken from the end of the circuit) ie Ze +(R1+R2).

Ok

Well i think ive calculated it right. measured Earth loop Impedance is 1.08. my r1 + r2 = 0.05. So ze = 1.03 so..

230/1.03= 223.3 ka..

Yup Pretty poor earth.

But this is a college test fortunatly and main protective conductor is only small as the circuit isnt used to power anything simply for testing purposes.

Cheers Guys

A

If you did this at college on a rig Your 1.08 ohms figure is too high but that is probably because it was not a true Ze taken at the distribution board but just taken from a plug socket that your rig was connected to. ie more of a Zs figure.
And be careful that you always change amps to kA as that is what is usually asked for on the certificate.
 
Last edited by a moderator:
Highest PFC will be voltage divided by Ze, but isn't it the lowest PFC that you are actually interested in - to to know if the minimum disconnection times for the protective device are met. If this is the case, do you not want voltage divided by Zs (taken from the end of the circuit) ie Ze +(R1+R2).

.

Max Zs confirms your disconnection times, not minimum PFC.

You need to know the maximum fault current that could flow to ensure
that switchgear and breakers etc can withstand the bang:) - this is found
at the origin.

You can also measure PFC at remote boards if you wanted to downgrade
the breaking capacity of your MCBs at that board.
 
Max Zs confirms your disconnection times, not minimum PFC.

.

Your max Zs will give you your min PFC though ;) (I was thinking of similar things i have been asked at college and wondering if the OP had been asked the same). I know it is Zs figures that are quoted in appendix 2 of the OSG though not PFC's.

Thanks for the 3rd point though i hadn't thought of that :)
 
To be honest, this discussion is a bit irrelevant as your PFC is most likely
to be your PSCC - (ie. L - N or L - L) and you're not gonna be calculating
that, so Ze/Zs/R1+R2 don't come into it.
 
Last edited by a moderator:
It's all very well quoting guidance note 3, care to explain how you'd do it?:)

You'll have noticed GN3 doesn't tell you how.


Ok then how would you answer this type of exam scenario or what about if it was real world scenario?

During a PIR on small comercial unit it is unpracticable to isolate the main switch, how can you ascertain a value of Ze? You have tried enquiry but no one will answer the phone? :mad:
 
Ok then how would you answer this type of exam scenario or what about if it was real world scenario?

During a PIR on small comercial unit it is unpracticable to isolate the main switch, how can you ascertain a value of Ze? You have tried enquiry but no one will answer the phone? :mad:

Measure it.

The only limitation is that you can't remove the earth for a true reading, you put this down under limitations.
 
Ok then how would you answer this type of exam scenario or what about if it was real world scenario?

During a PIR on small comercial unit it is unpracticable to isolate the main switch, how can you ascertain a value of Ze? You have tried enquiry but no one will answer the phone? :mad:

Keep trying the phone - coz if they won't let you open the main isolator, you shouldn't have the cover off the board in
the first place:)

Failing that, measure it with the earthing conductor connected and mark as limitation.

Everyone is arguing the ---- but no-one has come up with an answer yet - How can you
possibly calculate it accurately?

Or CALCULATE it using Uo and your measured Pefc and record this as a limitation. :cool:

If you've measured Pefc, you might as well have measured Ze while your there and mark Lim:)
 
Last edited by a moderator:
Keep trying the phone (and what do you think they'd say if they answered it?)- coz if they won't let you open the main isolator, you shouldn't have the cover off the board in
the first place:)

Well if your engaged in this sort of work lets assume you have the level of competence to do it. So not a problem. Or else how you going to measure Pfc??

Failing that, measure it with the earthing conductor connected and mark as limitation.

Everyone is arguing the ---- but no-one has come up with an answer yet - How can you
possibly calculate it accurately?
How accurate does it need to be??


If you've measured Pefc, you might as well have measured Ze while your there and mark Lim:)
Well you can re-decorate while your there as well but why do things you don't need to ?? :(
 
Last edited by a moderator:

Reply to Prospective Fault Current in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top