Ze may be calculated by:
measurement
enquiry
calculation
It's all very well quoting guidance note 3, care to explain how you'd do it?
You'll have noticed GN3 doesn't tell you how.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Prospective Fault Current in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Ze may be calculated by:
measurement
enquiry
calculation
It's all very well quoting guidance note 3, care to explain how you'd do it?
Whilst proving you have a reliable earth coming into the property which hasn't been supplemented by a gas, water or any other extraneous conductive part which has been bonded to the main earthing terminal.
Ok
Well i think ive calculated it right. measured Earth loop Impedance is 1.08. my r1 + r2 = 0.05. So ze = 1.03 so..
230/1.03= 223.3 ka..
Yup Pretty poor earth.
But this is a college test fortunatly and main protective conductor is only small as the circuit isnt used to power anything simply for testing purposes.
Cheers Guys
A
Highest PFC will be voltage divided by Ze, but isn't it the lowest PFC that you are actually interested in - to to know if the minimum disconnection times for the protective device are met. If this is the case, do you not want voltage divided by Zs (taken from the end of the circuit) ie Ze +(R1+R2).
.
Max Zs confirms your disconnection times, not minimum PFC.
.
It's all very well quoting guidance note 3, care to explain how you'd do it?
You'll have noticed GN3 doesn't tell you how.
Either volunteer for out of hours or put it down as a limitation.
Ok then how would you answer this type of exam scenario or what about if it was real world scenario?
During a PIR on small comercial unit it is unpracticable to isolate the main switch, how can you ascertain a value of Ze? You have tried enquiry but no one will answer the phone?
Measure it.
The only limitation is that you can't remove the earth for a true reading, you put this down under limitations.
Ok then how would you answer this type of exam scenario or what about if it was real world scenario?
During a PIR on small comercial unit it is unpracticable to isolate the main switch, how can you ascertain a value of Ze? You have tried enquiry but no one will answer the phone?
Or CALCULATE it using Uo and your measured Pefc and record this as a limitation.
Well you can re-decorate while your there as well but why do things you don't need to ??Keep trying the phone (and what do you think they'd say if they answered it?)- coz if they won't let you open the main isolator, you shouldn't have the cover off the board in
the first place
Well if your engaged in this sort of work lets assume you have the level of competence to do it. So not a problem. Or else how you going to measure Pfc??
Failing that, measure it with the earthing conductor connected and mark as limitation.
Everyone is arguing the ---- but no-one has come up with an answer yet - How can you
possibly calculate it accurately?
How accurate does it need to be??
If you've measured Pefc, you might as well have measured Ze while your there and mark Lim
My point was that you can't calculate Ze.