I am fitting a Heat only boiler that just serves the radiator circuit, the boiler has its own dedicated block terminal connector on the PCB but I cannot connect the pump to it as we normally do, the pump is a commercial type and Worcester Bosch have stated it will damage the PCB because of the excessive load/current drawn by the pump.


W-B have advised fitting a relay to protect the boiler electronics. A work colleague has emailed me a picture (see link below) of one a sparky wired for him in similar circumstances but that's where the fun begins, can anyone please help me with a simple wiring schematic on how to install this particular relay to serve both pump/boiler and the other items listed below which may or not be relevant in relation to the relay


Other items fitted which may be relevant:


Honeywell RF2 Pack 1 RF Programmer and room stat

Honeywell T4360 Frost Thermostat

Honeywell L641B Pipe Thermostat

Relay image link: dav - https://ibb.co/nLwAUb

Thanks in advance for any help


Ps. I'm hoping it’s just a simple case of some knowledgeable soul identifying the Supply & Load side of the relay!
 
The top is power in, the bottom is power out.
A1 and A2 are for your control wires the rest are for what you want switched.
 
A1 and A2 are the coil. then 1 switches to 2, 3-4, 5-6, 7-8
 
The top is power in, the bottom is power out.
A1 and A2 are for your control wires the rest are for what you want switched.

Thank you both for the swift replies. As you are aware I am not a sparky, I do however have knowledge of heating controls, but both anwers are confusing me a little, can either of you chaps post me a visual link of a wiring diagram as I can understand this better, sorry to be a pain :/
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.
 
Slightly the connections are correct the discription is in error. What you have is an electricly controlled switch. When power is put onto terminals A1 A2 this causes a coil of wire inside to become a big magnet and thus the insides of the switch move. If A1 A2 were a CONTACT and not a COIL then it would short stuff out, big bang and a repair bill.

As stated above wire A1 A2 to the boiler in place of the pump and all should be good.
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.


Apologies but can you just clarify, A1 & A2 are permant live & neutral from the breaker? I think i understand the rest of your guide
 
Get the wiring diagram for the boiler, identify the pump on the diagram for the boiler, connect A1 A2 where the pump is shown the on the wiring diagram for the boiler. Connect the rest as stated above
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.

Also thank you too Spinlondon for taking the time and trouble to help
 
Yes I wrote contacts A1 and A2 when I should have written terminals A1 and A2.
 
Get the wiring diagram for the boiler, identify the pump on the diagram for the boiler, connect A1 A2 where the pump is shown the on the wiring diagram for the boiler. Connect the rest as stated above

Update

To UKMeterman and spinlondon repectively, I have attched a basic wiring diagram below that I created in Microsoft Paint, can either of you please tell me if I have interperated your wiring guide incorporatiing the 'Contactor' switch correctly?

Thanks

Link: PROPOSED PUMP WIRING DIAGRAM - https://ibb.co/jUGgpb
 
No.
You got from ‘Boiler to external pump connections’ to terminals A1 and A2 correct.
You got terminals 4 and 2 to external pump correct.
The power to terminals 1 and 3 has to come from another source (preferably the same source as supplies the boiler).
 
I hope this explains:
A01D4C7D-C32D-4B06-873D-02FA3FD17C2A.jpeg
Top FCU has whatever fuse is recommended for the boiler (3A?).
Lower FCU (13A?).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Devon

Thread Information

Title
Protecting a boiler with a relay
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
22

Thread Tags

Advert

Thread statistics

Created
Harry Palmer,
Last reply from
Harry Palmer,
Replies
22
Views
3,249

Advert

Back
Top