Hi,
I am tasked with switching some special FX kit we have over to 24v ac, from 12v dc. Purely to achieve longer cable runs with lesser volt drop.
We have these transformers: link
Which are bonded to earth and powered via a MCB and RCD (we work with water) protected feed, as with all our kit.
But in the assembly I currently have, there is no protection or bonding on the 24v side. Should there be? What is the regulation? It's a double edged sword for us as if I add a 24v ac breaker, or simple fuse, I run the risk of inrush current tripping/blowing. Not ideal for special FX designed to operate repeatedly on cue! And the control box could one day be running 2 solenoids, the next day 20.. So matching protection to the current demand is problematic also. Should we instead use a over-current protected power supply - or will that also potentially break the circuit due to switching multiple solenoids?
And should the earth from the 24v solenoids be bonded to the mains earth?
Thanks in advance for any guidance.
Well what strikes me is any attempt to bond to earth from the 24v side to the 240v side would be unwise. If you think about it a fault on the 240v side earth could travel through to the 24v side causing abnormally high voltages. Again with water involved (although I can't quite visualise what your are meaning) Notionally anything above 50v a.c. is considered dangerous. Therefore I would suggest you would be aiming for a situation where you have SELV so that the earth is separated from the ELV side. Ah just looked at your link for the transformer which is an isolating transformer, so you don't want to undo the "isolating" safety feature by connecting the earth on to the mains from the ELV side.
If there is water involved I would use 12v SELV.
Thanks but there are two requirements to keep in mind.
1) It has to be safe, within regs.
2) It has to perform the intended function.
There are big problems switching several solenoids in parallel using 12v due to the inrush current and the lengths of cable. 12v limits the distance and number of valves we can switch.
For the same reasons, irrigation systems commonly use 24v ac. That is effectively what we're re-creating here, albeit for a different purpose.
We use 2.5mm cable. Typically 20m from the power supply to the first solenoid. Another 20m to connect to all solenoids, then 20m back to the power supply. So we create a 60m 2.5mm ring circuit back to power supply, with all the valves branched off from that. I think with 12v power supply pushed up to 13.5v, we still only saw 8v on the far side of the circuit. That leads to staggered and intermittent operation of the valves.
Thanks, I had assumed that it would be odd to bond primary and secondary earth. So, no earth on the 24v side then? Looking at the valves, some have earth pins, some don't. I assume the ones that do are because the are brass, and the same body is used for 240v versions.
As it is ELV, is there any requirement to bond at all?
I'm only concerned with not being criticised really. The water element is the reason we use lower voltages, as it essentially removes the risk. 24v can in theory be dangerous. But 24v also passed through water... water is actually rubbish at carrying current.
Still leaves a question mark over circuit protection though. 24v can still get hot and start a fire so I feel there should be something in place just in case for whatever reason, it were ever to get that hot. Can't think how/why it should but..
Can you draw a sketch diagram it's hard to see exactly how all this works and when you say 'to regulations' you do realise this is out of the scope of the BS7671, your treading into the realms of machinery control etc even though your just switching solenoids - the requirements to design will be similar, the earthing arrangements are flexible on extra low voltage and denoted on how you arrange your fusing, strapping one leg down of the 24v will change the acceptable fusing arrangement that is permitted, you should be looking into the BS60402-1 for guidance on that, it will also show you the colour coding requirements of control wiring and that of power circuits.
Most transformer chassis are earthed through, it is common in control equipment to strap down one side of the output to common earth, this poses no issues even of that you have mentioned, I often strap down on the 24v side as this allows for simpler and easier fault finding if you can reference the control voltage to any local earth, don't mix this up with an Isolating transformer like found in a shaver outlet where the output has no earth reference thus safe to use in a bathroom even if it went faulty.
Sorry on the move - got this project with stupidly short lead time so rushing around.
It's very simple though. Mains to transformer. Then the 24ac output is sent around a ring circuit of 25mm cable, with each solenoid taking poor of the ring (wired in parallel). At present there is no bonding on the 24v side at all. It could in theory make a structure/person live if damaged and exposed - but of course, only 24v so probably no one would notice unless they were investigating using their tongue...
The other aspect is that the valves for the most part don't even have an earth wire/terminal. See first few seconds of this video for a similar valve type. No earth..
If there was nothing specific saying it should be bonded, I would be happy to simply not bother. They will be mounted away from people on a aluminium truss frame, which is itself grounded, like all steel/alloy structures.
Just to add here, there are other issues that must be understood and accounted for when designing control systems and that is floating voltages, example - you can have a DC speed drive card that puts out a 0-10v reference to a pot' so the user can control the speed of a motor, some drive cards do not have galvanic isolation and thus a floating voltage can appear on the 0-10v, this will not interfere with how the drive works but can be hazardous to the user especially if the pot becomes damaged or gets wet, they can receive nasty belts or worse from what is a 0-10v signal device.. I have seen voltages on these systems as high as 230v plus so heed caution, having said that if all your doing is creating an extra low voltage to operated solenoids then this shouldn't be much of a concern.
If you think about it, if a fault occurred on the 24v side and one went down to exposed metal work then if you have not strapped down either leg then the person would have to be in contact with both the metal work and the other un-grounded leg to get a PD of 24v which is not going to give them any real noticeable shock, strapping one leg down gives a few advantages in that a damaged cable would have a higher chance to blow a fuse and faulting the circuit can be done more quickly although the latter can still be done by simply grounding one leg for testing purposes only.
The call is yours and should be based on the type of control system, the equipment been used, the risk of problems occurring be it faulty equipment or a higher risk of damage/wear and tear etc and the ability for the circuit to respond accordingly to maintain safety.
I cannot tell you what is the best solution for your particular circumstances as it varies widely but which ever method you choose you need to understand what fusing solutions that go which it.
Just an additional note here, the special effects industry is heavily regulated and as I have no insight to what you are actually doing then all of which I have explained may not be applicable to your situe', I would seek the relevant regulations to cover this sector and if there is explosives etc used then there will definitely be some very strict guidelines and standards to follow even in the control side.. you can imagine you do not want a device going off by accident because of a bad control design.
Like any industry, all the common parts are heavily regulated. So explosives, yes of course. But we deal solely in water FX which is so niche, there is nothing specific. Other than obviously basic electrical good practice and water contamination guidelines etc.
Fair do's ... yes you did mention it earlier but was unsure how far you went with effects, even water systems will have heavy regulation if they are pressurised or pressuried gasses are used, any system that component failure or control failure could cause serious injury or death, if there is little pressure used then possible not an issue.
@darkwood you say it is not to be confused with shaver transformer (isolating type) but it does say on the transformer link it is EN 61558-2-6 which I understand is isolating tranformers, and or SMPS types as well. Slightly lost here on BS EN standards. As I can't afford to buy them all let alone the time to read and digest.
This is totally off the wall and related in a tenuous way. Back in the eighties I was involved with SFX and a couple of old boys I worked with showed me how they recreated machine gun tracks across the floor in war pictures back in the fifties. We were down the Lot at Pinewood and they laid some parallel charges beneath some leaf cover with each one wired back to a row of nails on a plank of wood, a wire was taken from a car battery and with the bare end it was flashed along the nails creating a machine gun track, brilliant:D
What I meant was not to confuse it with how a shaver outlet is connected on its secondary side, yes TX's in control equipment are often isolating as is the one he has chosen but how you arrange the earthing is down to the designer, Isolating TX's can be strapped down on the secondary if required, output voltage is often key to whether this is a safe method and as 12 or 24v is extra low voltage then it is the choice of the designer.. if you think about it just take a typical onsite 110v TX and look how the earthing is done.
Well this is where I am with my thinking too. There is no way of anyone accessing the valves/connection points themselves, so it's basically just metalwork the system is attached to that could transfer current to within reach or a person. And that metalwork is earthed to ground in anycase. Fault finding is also straight forward there is a twist lock connector every 8m cable of the ring circuit so it can just be broken into smaller parts and tested that way. Would only take minutes.
I am indeed most worried about circuit protection. What would you use on the 24v circuit? It needs to be something that won't trip/blow due to the inrush current when the solenoids are first energised (could be 20 at once). The number of valves and therefore the load varies though. But obviously won't exceed the capacity of the cables.
Is there an MCB that would be suitable for 24vac use? We have only used fuses previously (the power supplies were fused). These 24vac are not. Would prefer MCB to fuse as it's faster and instant reset.
This is where you pass the boundaries of needing helpful advise and are really requiring a design doing , I have little info to go on as I have no ratings for valves or peak inrush nor do I have frequency or duration or usage all of which can effect the requirements of the front end TX, I also don't want to get drawn into actually designing it for you, it would be an idea to set up a test bench and design it to the worse case scenario and get a TX oversized for your needs, although you will have to consider on sight power supplies too, you don't want to be tripping them when you plug in the main TX.
There is a lot to consider when you design such a project of which some I haven't even touched on, if the solenoids are 12v DC then you have to consider high voltage spikes as the solenoid field collapses when switch off, this can do a lot of damage to control equipment if you don't put in some form of flyback diode.
Oh the same kind of shenanigans still happen in the SFX world ;)
Generally even when something is lashed up in a hurry and not perhaps 'ideal' common sense prevents actual danger. I'd say pretty much everyone I know in the industry is very capable of making things safe, regardless of whether or not a chap holding a clipboard would agree it is within regulation.. I could give some humorous examples but best not to tell tales.. I will go as far as to say if it starts to rain outdoors, a lot of non weatherproof equipment is instantly upgraded to IP68 with the use of bin liners etc.
Our kit is pretty basic really. We use a PLC to handle control, which is EMF sensitive. But we then use the on board relays to switch over larger relays. So nothing feeds back to anything sensitive. The PLC is on an independent circuit altogether.
We use relays with flyback diodes too. Never had any issues. I have heard it's a far greater issue with higher voltage solenoids, or other inductive loads. I assume because the lower voltage coils can only build a flyback charge that is capped below the level at which it can do much if any harm. It's tricky for us to do these things 'perfectly' as the reality is the kit is all modular and gets hooked up in different configurations all the time. We take basic precautions to make it as reliable as possible, and certainly to make it safe.
As for circuit protection - seems I could just buy a load of these at different ratings and swap over to the rating most closely matched to the demand on the circuit each time (without exceeding cable limits). We do testbed the systems each time so no issue to fire the solenoids on and off a hundred times to make sure they don't trip it. In addition to testing the operation of the breaker within the circuit.
https://uk.rs-online.com/web/p/mcbs/7913290/
You gave a link that shows a 100w TX 400/230 - 24ac
If you look at the product image it does tell you that the output fuse will need to be 4amp gG, this may blow with multiple solenoids so a 4amp gM may be wiser, if this still has issues then you need to consider a larger TX, if you fuse the secondary side correctly then the primary can be fused as short circuit protection only and you can uprate it to suit the inrush requirements, I would strap down your secondary on one half and fuse the other side as suggested on the TX - ohms law gives us that rating fuse of 4amps.
Can't you just fuse each valve? I know it's more work, but it would scale with capacity that way. If you had a dead short in a single valve, it would blow the fuse locally at the valve, rendering it dead, but keeping everything else alive and working for your FX.
If there is a dead short in the cables, well...you gotta ask yourself what over current can your transformer take on the secondary side before it dies, is that 4amp on the label? You would have to fuse low anyway to protect it, and fuse the solenoids even lower to at like 1amp so a failure can't pop the main fuse...
Hi bud,just three questions...
What is the holding current or rating on those valves?
Can you not use a pilot operated valve,to reduce current?
When is Waterworld II being released?
Agreed, the transformer is what needs protecting here, not the cable. The 100VA tranny with its 4A maximum output would be toast before any damage was done even to one leg of 2.5mm² let alone a ring. The valve wiring and coils are a different matter, maybe there is value in putting small fuses in the tap-off points.
Ideally you should fuse to fully protect the transformer against continuous overload (i.e. it should eventually trip before the winding exceeds a safe temp) but as it has high thermal mass the protection can be relatively slow. A thermal CBE (Circuit Breaker for Equipment) might suit - you don't need magnetic protection as the short-circuit current is small compared to a mains circuit and might not even be high enough to reliably trigger a magnetic trip if the fault is at the end of a very long run. Not having the instant magnetic reponse will help avoid nuisance tripping on inrush.
Have a look at something like http://www.e-t-a.co.uk/fileadmin/us...rungsautomaten/Thermisch/2_eng/D_1658_ENG.pdf
Thanks,
The issue then is if a fuse blows, it's 8m up in the air above a giant pool of water. So best to keep protection at source of the circuit.
17va holding. And there will be 9 on the circuit. The problem with pilot op valves is that they are prone to failing to close of even a tiny bit of debris finds it's way through. The solution is to use a direct acting valve, as we do. But yes, direct acting valves do have up to 10x the current draw.
As for waterworld 2... I think it took so long to break even the first time it's one film there may not be a sequel of ;) But it's an excellent example of how expensive doing anything with water is. Many films and TV shows end up cutting intended features when they see the cost of making water tanks/fx safe. Although it's also true that sometimes 100k will get spent on something that never actually makes the final edit.. I love my job - sometimes.
Stamford
Business Name
Aquatic Impact Ltd
Protection and earthing of 24v ac circuit to energise solenoid valves
Deuce,
Deuce,