I'm familiar with current regulations for protection of meter tails over a certain (e.g. 3m) length, but what about a periodic inspection of a fairly old installation?

The installation in question has a Henley block, then an old isolator - looks to be perhaps 40+ years old, with no fuse - feeding a distribution board in a remote part of the house (in addition to an old fuse board close by the meter, also from the Henley block). The isolator looks in good condition otherwise. The distribution circuit is 10mm2 twin & earth, and maybe 15m or so long.

If this was acceptable practice at the time, does it need more than a C3 code now on an EICR for missing protection of long tails?
 
Last edited:
could be a potential danger if 10mm tails are protected only by the DNO fuse of 80A or 100A, in which case it's a code C2. if the tails show no sign of overheating, then you might give it a C3. your call, mate. personally, i'd quote for a 50A fused (or MCB) isolator. they're not a huge cost.
 
Thanks Tel. Actually I don't know the fuse size in the DNOs fuse carrier, and will only find out later, if I end up replacing the isolator (or the other fuse board). However, your post made me realize that because the tails are only 10mm T&E, probably it needs a C2 for that anyway with the mix of installation methods applicable. I'd still be interested in comments that suppose if the tails were larger, e.g. 16mm T&E clipped direct with an 80A DNO fuse, was that once OK and thus only need a C3?
 
suppose if the tails were larger, e.g. 16mm T&E clipped direct with an 80A DNO fuse, was that once OK and thus only need a C3?



AGREE.
 
Re: Protection for >3m tails

Due to the fuse board being remote there should be a local fuse adjacent the Henley Block anyway but due to size of cable I would C2 it and also add no RCD protection on cable as a C3

- - - Updated - - -

Due to the fuse board being remote there should be a local fuse adjacent the Henley Block anyway but due to size of cable I would C2 it and also add no RCD protection on cable as a C3
 
i thought the max length of tails was a dno , therefore an ESQCR , regulation.
you could argue it falls out of the remit of a inspection to bs7671.
if all other aspects of the tails are ok ( correct size , adequately supported / protected )
exactly which reg do you code against ?
mention it in the report , but without code.
 
i thought the max length of tails was a dno , therefore an ESQCR , regulation.
you could argue it falls out of the remit of a inspection to bs7671.
if all other aspects of the tails are ok ( correct size , adequately supported / protected )
exactly which reg do you code against ?
mention it in the report , but without code.


i agree up to a point, as regards the DNO and ESQCR comment, but you still have 10mm tails protected by an over sized fuse, which, IMO, warrants a code, even if only a C3,
 
Thanks for the additional replies.

To sum up, if I’ve understood correctly, for tails over the length permitted by the DNO (typically 3m), suggested EICR code:


Cable not mechanically protected, e.g. T&E in walls
Cable is mechanically protected, e.g. SWA
Conductor size too small for DNO fuse rating, taking account of installation method(s)
C2 – needs fuse/MCB
C3 – recommend RCD
C2 – needs fuse/MCB
Conductor size OK for DNO fuse rating, taking account of installation method(s)
C3 – recommend RCD
No code – though does not meet ESQCR

This always assumes you know the actual DNO fuse size, e.g. a 100A carrier will often have a lower rated fuse fitted, which might not be easily checked.
 
not 100% happy with the C2's. if the cable is, say, 16mm on a 100A DNO fuse, and has been in situ for years without any signs of damage, i'd lean more towards a C3.
 
I'm inclined to agree, if 16mm2 cable CCC can be as high as 94A for reference method E, it is not that far short of the 100A. The trouble with having just three codes to choose from, with something marginal, I find it can be difficult to decide which code.

A different example I’ve come across a few times recently is small amounts of visible (exposed) live cable or terminals on the suppliers equipment, e.g. on the fuse carrier or meter tails, trying to decide if it should be a C1 rather than C2.
 

Reply to Protection for >3m tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
983

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
949
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top