Been reading up on the regs regarding protective conductors and doing a few calculations for imaginary circuits.

What is the point in having Table 54.7 in 543.1.4 if the values contradict those calculated using the adiabatic equation are much lower?

Is 54.7 just there as a time saver so you can just comply with that if you can't be bothered to do the calculations?

Please excuse my confusion, I've just spent hours with the books trying to work out how 2.5mm T+E with a 1.5mm cpc is compliant, as it contradicts the table!
 
Yes the table is there for people who can't be asked to conduct the calculation.
As indicated by the first line of 543.1.4.
 
The worst possible case, where a protective conductor provides earth fault protection for a number of circuits, such as an earthing conductor then you have a choice :
1/ Use the adiabatic formula 543.1.3
or
2/ By selection from table 543.1.4

I've always wondered why there was such a large difference between the calculated value and the tabulated value.
More guidance is given in 543.1.1 in that the minimum values allowable by calculation where the protective conductor is effectively separate from the live conductors, are 2.5mm2, protected and 4.0mm2 non-protected.

However, to cover all possible scenarios such as extra mechanical protection or/and non-competence of installation owners etc., table 54.7 is provided.

There is one partial exception where the protective conductor is the earthing conductor, usually associated with TT systems, providing protection for the whole installation and then reference to table 54.1 is made.

In other words, as mentioned earlier, if your fingers struggle using (√) the square route function on a calculator then use the table provided .
 
There is no contradiction on protective conductor sizing, only choice!! Those sizes stated in 543.1.4 will cover your earthing requirements in all circumstances. While 543.1.3 will give you a minimum size to cover your earthing requirements in a specific circumstance!!


As others have stated, you have a choice of which Reg to use. The adiabatic formula is useful when you have an existing conductor size that maybe difficult to replace or upgrade. Using the formula, will tell you if the smaller CSA conductor will still comply ....or as it maybe, ...Not!!!

Even the adiabatic formula has a safety margin, but we won't go there. All you need to understand, is that you are given a choice of determining your protective conductor size...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Protective conductor size... 2 contradicting regs?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
DNS1,
Last reply from
DNS1,
Replies
6
Views
1,887

Advert

Back
Top