Hi everyone
Im fairly new to electrics and the forum, im looking for some help on testing of a PME supply, It is my understanding that because the neutral and earth are combined the psc and pfc should measure the same. (as told by my assessor from Elecsa) I have a pfc of 3ka and a pscc of 2.4kk. Im using a fluke multi purpose testor and wondering i if it is faulty. Many thanks in advance for any assistance
 
hi Scotsparky

It has a large lable saying pme below the fuse carrier and the seal has previously been cut, which allowed me to see the combined neutral / earth connection
 
Hi Baza,

I wouldn't worry about it too much.

Firstly, your PSCC is Line to Neutral and, at 2.4 KA, gives an impedance of 0.096 ohms.

Your PEFC is Line to Earth and could include parallel paths through bonding of extraneous parts - at

3 KA this gives an impedance of 0.077 ohms.

A difference of approx 0.02 ohms - basically negligible:) and could be down to the bonding, leads,

connections.

Your Ze reading of 0.11 gives a fault current of approx 2.1 KA - but this is with the earthing conductor disconnected from the MET.
The difference in CSA of the tails and the earthing conductor could give the slight discrepancy in this reading


I wouldn't worry about it - just record the highest:D - the readings seem fine to me.
 
Hi everyone
Im fairly new to electrics and the forum, im looking for some help on testing of a PME supply, It is my understanding that because the neutral and earth are combined the psc and pfc should measure the same. (as told by my assessor from Elecsa) I have a pfc of 3ka and a pscc of 2.4kk. Im using a fluke multi purpose testor and wondering i if it is faulty. Many thanks in advance for any assistance


Exactly as WayneL says, pefc should be measured with the earthing conductor connected to gain the worst case comparison for your protective devices, if there are parallel earth paths then its going to be higher than pscc
 

Reply to pscc and pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Yeah I doubt it's normally an issue. Split load boards and SWA incomers are likely the only trouble.
Replies
16
Views
3K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
D
  • Question
PFC
If you are bored and have a half hour to watch a semi-advert video, this has a very graphic illustration of protective devices in action:
Replies
6
Views
2K
  • Question
I haven't resolved it yet, but I have a plan to ask an electrician to come and have a look at my wiring and let him tell me if it's safe to leave...
Replies
8
Views
2K
  • Question
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks