H

hodaire

got a submain feeding a consumer unit, bit unsure with the pscc, pefc and pfc

pscc would be voltage / resistance of live and neutral cables plus the ze
pefc would be voltage / zs

how do i get pfc, is this just the highest of the 2 readings?

if i was fitting a 3 phase board pscc would it just be 400 / resistance of live and neutral cables plus the ze but pefc would still be 230 / zs?
 
got a submain feeding a consumer unit, bit unsure with the pscc, pefc and pfc

pscc would be voltage / resistance of live and neutral cables plus the ze
pefc would be voltage / zs

how do i get pfc, is this just the highest of the 2 readings?

if i was fitting a 3 phase board pscc would it just be 400 / resistance of live and neutral cables plus the ze but pefc would still be 230 / zs?

Pefc - Prospective earth fault current is measured between line and earth (with all bonding in place) if you have a 3 lead tester connect Green to Main earth at MET black to incomming neutral on main switch and finally red to incomming line on main switch then measure using a PFC tester on 20kA range.

Pscc - Prospective short circuit current is measured between Line and neutral - connect bothe the green lead and the black lead to the neutral, then finally the red lead to the line and again measure using a PFC tester on 20kA range.

which ever is the highest of either Pefc or Pscc are recorded on the test sheet as the PFC prospective fault current for that installation.

If you do not possess a PFC tester than do the test a described above but use an ELZ tester and calculate the both the Pefc and Pscc.


Where pefc = measured voltage L-E / measured impedance L to E

Pscc = measured voltage L-N/ measured impedance L-N

again whic ever the highest record as your PFC
 
Don't forget, "For three-phase supplies, the maximum balanced Prospective Short-Circuit level will be, as a rule of thumb, approximately twice the single-phase value."
 
Last edited:

Reply to pscc, pefc and pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
999
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top