So should I test between phase and neutral, phase and earth then record the higher figure on the test sheet?
In therory yes, However; with both main and supplementry bonding in place on Water, Gas, Oil, structral steel, etc, there will be additional parallel paths for currents to flow down.As an extra a TN-C-S system should have identical values for both as it's a PEN conductor.
PFC is your Prospective Fault Current.
It made up from the higher readings of two tests.
PSCC = Prospective Short Circuit Current. Tested between LIVE conductors. L1,L2,L3 & N
PEFC = Prospective Earth Fault Current. Tested between Line conductors to Earth. L1-E, L2-E, L3-E
On single phase installations PEFC is usually higher.
On three phase installations PSCC is usually higher because it's at 400v rather than 230v.
PFC should be tested because all parallel paths for earth are taken into account. When testing Ze you remove all parallel paths.
Your trying to find the maximum fault current that can flow within you installation.
Ohms Law. Less resistance more current.
Can you explain why?Not really, the pscc is usually higher, although as Lenny points out, on a tncs system they should be about the same.
Parallel paths will cause the current to increase not decrease as there is a lower impedance.
With a tncs as the neutral is effectively the same conductor as the earth you would expect similar results, but because there are parallel paths for earth then the pefc will be higher (due to lower impedance) than the pscc (just as a tested Zs is usually lower than a calculated one)