Hi all. Can someone please explain the difference between the two. Also if I know the Ze on a single phase installation is it a simple Ohm's law calculation to find out the Pscc?
 
Prospective Fault Current (PFC) is the highest value of the two readings of Prospective Earth Fault Current (PEFC) and Prospective Short Circuit Current (PSCC)

PEFC is measured between L&E, PSCC is measured between L&N. On a 3P install PSCC is doubled (as a rule of thumb) as the highest fault current will always be between the phases, unless you test meter can measure between phases.
 
PFC is your Prospective Fault Current.
It made up from the higher readings of two tests.
PSCC = Prospective Short Circuit Current. Tested between LIVE conductors. L1,L2,L3 & N
PEFC = Prospective Earth Fault Current. Tested between Line conductors to Earth. L1-E, L2-E, L3-E
On single phase installations PEFC is usually higher.
On three phase installations PSCC is usually higher because it's at 400v rather than 230v.
PFC should be tested because all parallel paths for earth are taken into account. When testing Ze you remove all parallel paths.
Your trying to find the maximum fault current that can flow within you installation.
Ohms Law. Less resistance more current.
 
which means the neutral and earth share a common cable from sub station upto the cutout, then seperates into neutral and earth from there.
 
As an extra a TN-C-S system should have identical values for both as it's a PEN conductor.
In therory yes, However; with both main and supplementry bonding in place on Water, Gas, Oil, structral steel, etc, there will be additional parallel paths for currents to flow down.
Essentially we create (with bonding) a larger Earth back to the star point of the transformer.
 
PFC is your Prospective Fault Current.
It made up from the higher readings of two tests.
PSCC = Prospective Short Circuit Current. Tested between LIVE conductors. L1,L2,L3 & N
PEFC = Prospective Earth Fault Current. Tested between Line conductors to Earth. L1-E, L2-E, L3-E
On single phase installations PEFC is usually higher.
On three phase installations PSCC is usually higher because it's at 400v rather than 230v.
PFC should be tested because all parallel paths for earth are taken into account. When testing Ze you remove all parallel paths.
Your trying to find the maximum fault current that can flow within you installation.
Ohms Law. Less resistance more current.

Not really, the pscc is usually higher, although as Lenny points out, on a tncs system they should be about the same.
 
With tncs, the earth & the neutral are the same conductors so you would expect the same reading.But as its name sugests, with a tns system the neutral & earth are separate and so would have a diferent resistance.Usually (not allways) the earh has a greater resistance than the neutral and so the current flowing to earth in an earth fault would be less than that flowing through the neutral in an l/n fault.
 
I would think the comparison between pscc and pefc on a single phase depends very much on the earthing arrangement. For the testing of a pfc bonding should also be in place, unlike when testing Ze.

With a TT the pscc will almost certainly be larger due to the high earth electrode resistance reducing the pefc.

With a tncs as the neutral is effectively the same conductor as the earth you would expect similar results,and because they have the same parallel paths

With a tns the earth to the transformer is separate from the neutral and will probs have a larger resistance than the neutral, so making the pscc more likely to be the larger. However, the parallel earths available to a pefc will complicate matters and so could bring it to a higher value. Making the case to test both a stronger one.

Edit must improve my proof reading !!
 
Last edited by a moderator:
No probs. I thought I'd read it wrong at first!

Don't worry about it - we all know what happened to the last person who never made a mistake...
 
With a tncs as the neutral is effectively the same conductor as the earth you would expect similar results, but because there are parallel paths for earth then the pefc will be higher (due to lower impedance) than the pscc (just as a tested Zs is usually lower than a calculated one)

The parallel paths are there for the pscc as well as the pefc, so you are reading the same thing both times.
So the results would be similar.
 

Reply to Pscc / Pfc confusion in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

T
  • Article
Solvent or push-fit? Can anyone explain why we have two different sizes of waste pipe for solvent weld and push-fit connectors? Why didn’t they...
Replies
0
Views
109
TonyR1
T
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top