I have just qualified as an electrician but am wanting to do my wiremans license and have been told to do some inspection and tests before doing the exam so that I can have a practical understanding of the system. With regards to this I did a PSCC test on a simple installation. Using a SUB DB, I connected my green clamp to earth bar, black clamp to neutral bar and red clamp to live incoming. All lock outs were in place and RCD's bypassed to eliminate tripping (I don't have a "no trip" function on my tester). I get a Ze reading of 0.41 ohms and a PSC of 640A. My question is why is the reading so low? Surely this should be in the kA range or does distance play a role i.e. from mini sub to testing location? It is a 3 phase installation so I am told I must double the reading. Is this correct?
Thanks
 
think you are confusing pscc with pefc. your pefc with a Ze of 0.41ohms should be 230/0.41 = 561A. pscc is measured between L and N ( single phase ) . you double that for 3 phase, or measure ph/ph., in which case the voltage would be 400.
 
Thanks guys for the replies. How much of an affect will it make if I am testing at a Sub DB. This is in a factory so won't be able to do the PSCC test at the main DB...production cannot be stopped. I do understand the double the reading for 3 phase. And yes I am measuring between L - N for the PSCC test. But from what I have read the further you are away from a mini sub/substation the lower the reading will be so I will use the 0.56kA reading.
 

Reply to PSCC Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top