Just started back testing after 3mths install work,its easy to forget things after a break.On the last pir we did 3 phase pscc was noted on meter then this measure was doubled and put on test sheet(as it was 3 phase) Now starting on this job the guy in charge does not double this measurement and i was going through all my test and insp. & n.i.c.e.i.c books to find this !!!!!!! I KNEW i had read this somewhere, could not find it in any n.i.c.i.c books but then EUREKA found quotation in the amicus guide to inspection & testing.Out of interest how do you guys record it??????? which is right or wrong
 
The doubled value is the value to be recorded.

Depending on your test equipment a 3 phase fault current can be tested directly to give correct value as opposed to the rule of thumb method.
 

Reply to pscc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Yes I noticed that too, although the Fluke 1664 that I use claims the same precision (it has a milliohms mode in the high current loop impedance...
Replies
18
Views
3K
Good advice...get familiar with the course as the books, videos are out there... Had to build a board with sockets, lighting to practice at...
    • Like
Replies
1
Views
4K
  • Question
A thermal camera is handy at times.
Replies
3
Views
1K
Thank you, in the motor controls I have experience with this has been the usual set up I am used to, apologies for my ignorance. I will have a...
Replies
2
Views
4K
I believe that if some how can go up on your wire size from the transformer to your place it would make a huge difference in your voltage...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks