The PSSC of a final ring circuit is 2KA so what is the min CPC size?

For PVC singles k = 115
CB 32A (BS EN 60898) will disconnect in 0.1 second
Fault current of low impediance = 2000A

S = square root of PSSC x PSSC x disconnection time (t) / Cable constant (K)

CPC size = 5.50mm (6mm cable)

So 2 x 1.5mm commonly used in final ring circuits is too small!

Earth fault loop impediance (Zs) is 0.4 Ohm (below the 1.5 ohm min)

By my calculations if an earth fault of low impediance was to occur anything less than a 6mm CPC would be damaged by the energy let through.

Should I now do as the regs say and consult manufacturers data for more accurate tripping times?
 
PSCC has nowt to do with CPC selection. If anything it would be PEFC, if it were at the origin. For a final circuit, divide the supply voltage by the circuit Zs to obtain (I).
 
I hope that is where I have gone wrong!

Actual it is where I have gone wrong fault current is related to Zs not PSSC.

The PSSC measures between phase and neutral which are 16mm at CU, then 95mm at distribution board.

CPC is 4mm from distribution board CB 50A to consumer unit. (This is a hotel).

During the calculation stage I worked out 1.5mm was big enough but though it a might get damaged during installation.


Thank you so much.

I can sleep easy now its 1.30 Am and I am in Thailand.
 
Are you in Thailand for this job your doing, or are you living there?? Oh, ...And careful, not too many girlfriends while your there, ...though they are very, very tempting lol!!!:tounge_smile:
 

Reply to PSSC & CPC size confusion in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top