Hey all, just looking at a house for a friend who has purchased after someone suggested by his surveyor looked at the wiring from CU in garage etc.. and said it's grey so it's new colours and all fine !
Just popped by as he's had 2 belts so far and tripping breakers and it's full to the brim of green goo, wiring looks to be original which would be 46 yrs old from house build, no records of install or any testing.
No main bond to water or heating pipes and he's asking about a possible rewire, so I checked a few bits while had an hour or so free this afternoon and he only has a main earth from TN-S MET to CU which is a MEM I've never seen before and PSSC gave a weird result of >2000 Ohms ?? Never seen that before.
IR on entire board is sub 0.46 MegOhms and individual circuits quickly looked at such as ground flr lighting and ring were around the 0.36 Meg Ohm level after a held press like it was slowly drying out the cables. He has had pokes from wall lights he took down due to him thinking they were dead if lighting MCB's off ! but found they had been fed through a hidden fused spur in a lounge fitted cupboard from a lounge socket up to a 3 gang light switch ! Ze was fine but as I say PSC / PSCC not reading right. Any advice ? Looking like a rewire to sort it as I think wiring is very old and not worth patching over with odd bits of new stuff. Thanks all.
Just popped by as he's had 2 belts so far and tripping breakers and it's full to the brim of green goo, wiring looks to be original which would be 46 yrs old from house build, no records of install or any testing.
No main bond to water or heating pipes and he's asking about a possible rewire, so I checked a few bits while had an hour or so free this afternoon and he only has a main earth from TN-S MET to CU which is a MEM I've never seen before and PSSC gave a weird result of >2000 Ohms ?? Never seen that before.
IR on entire board is sub 0.46 MegOhms and individual circuits quickly looked at such as ground flr lighting and ring were around the 0.36 Meg Ohm level after a held press like it was slowly drying out the cables. He has had pokes from wall lights he took down due to him thinking they were dead if lighting MCB's off ! but found they had been fed through a hidden fused spur in a lounge fitted cupboard from a lounge socket up to a 3 gang light switch ! Ze was fine but as I say PSC / PSCC not reading right. Any advice ? Looking like a rewire to sort it as I think wiring is very old and not worth patching over with odd bits of new stuff. Thanks all.