Hi all.

Could someone please confirm where to connect a 4-20mA pressure transducer to AI2 in the attached photo. I believe it’s terminals 7 & 8 but the pump is not responding at all.

Thanks.

[ElectriciansForums.net] PT Connection To Pump
 
Basically you have a circulation pump with an attached inverter?

The analog inputs are AI1 and AI2 you can use either, you’ll have to configure the inverter parameters to allow PID control as per page 17 onwards of the manual, have you done this? Depends on what your trying to do with it though.
 
Last edited:
Thanks for the reply.

AI2 has been configured in the grundfos go app for pump control via discharge pressure into a private water main. I've taken a 24V supply to the transducer from terminal 8 with the return from the transducer into terminal 7.

Screen is connected to gnd. The pump doesn't control to the pressure setrpoint at all.
 
Is there a jumper between 2 and 6 for start signal?
 
Yes.

Starting to think it may be an issue with airlocking around the transducer due to its position as part of the pump assembly. With the loop calibrator connected in place of the transducer, the pump responds as it should.
 
If the polarity is correct and the transmitter is healthy then I would say that’s the only thing it could be unless it has the wrong range of course.
 
Last edited:
Sorry for not following up.

Turns out the fault was due to airlocking around the PT. The new VSD didn't like the setup so I moved the PT further along the discharge pipework and it worked fine.

Thanks for the replies, nothing worse than when you start doubting yourself!!
 

Reply to PT Connection To Pump in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

P
  • Article
Baxi 105e pump head removal Hope you confirm something’s for me, boiler calls for how and ch but am not sure if pump is rotating, have checked if...
Replies
0
Views
72
Plipplop
P
Hi there , I wired it up following the instructions from similar model. Works great thanks for your help
Replies
4
Views
356

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top