Hi, any help would be greatly appreciated. I’ve been asked to wire up a second hand 3 phase pto generator to an existing generator switch (see pictures). What I would like some advice on is; 1. Should the generator have its own earth electrode or can it be earthed to existing electrode. 2 . Should the main neutral be kept separate from the generator neutral at generator switch ( I’m presuming it should). 3. I am worried the pto has no voltage regulator so worried the dairies electronics might get damaged if RPM is too high. Not sure if to take the job on, but would still like to improve my knowledge on this type of generator even if I don’t!! Thanks again for any help.
 

Attachments

  • [ElectriciansForums.net] PTO generator connection
    E752B796-C9F1-4821-A2D5-0AF51F260DB7.jpeg
    420.3 KB · Views: 55
  • [ElectriciansForums.net] PTO generator connection
    1FC42B4B-2854-4C95-9D35-F8016792E10B.jpeg
    417.7 KB · Views: 48
  • [ElectriciansForums.net] PTO generator connection
    02320B97-E2D1-454B-964B-400B4DF51B94.jpeg
    372.7 KB · Views: 43
  • [ElectriciansForums.net] PTO generator connection
    9D8D297F-1E55-438D-96C5-97FF3CD65B49.jpeg
    599.5 KB · Views: 39
  • [ElectriciansForums.net] PTO generator connection
    3C26BF0E-A22B-4C7B-9312-8AE6E1CE5265.jpeg
    429 KB · Views: 40
Wired up a few of these, although mostly single phase.
You need to provide earthing arrangements that would be adequate with the suppliers earth connected., but permanently connected in parallel.
All live conductors, which includes the neutral must be switched.
There should be a frequency indicator, rather than a voltage indicator connected to the generator. This either has a traffic light (red, amber, green) display or a single flashing amber light display, where the PTO speed is adjusted so that the light flashes very slowly.
These generators were usually supplied with change over switches, sized to the output of the generator. In a lot of cases these were not suitable, because the switch needs to be rated to match the maximum possible load, which was often much greater than the generator output.
An isolator should be fitted to the incoming supply before the changeover switch, which should be turned off before the C/O switch is operated. Looks like you already have this in place.
It can be handy to have an indicator lamp to show when mains power is restored.
Educate the farmer on how much tractor power these things can take. They think they take next to nothing, since the shaft can easily be turned before load is applied. Make sure they know better than to switch the C/O with the genny up to speed and a heavy load connected. I once saw a farmer do this, and the tractor was nearly flipped onto its side.
 

Reply to PTO generator connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We’ve recently completed the first and second fix of a barn conversion that is off grid with solar PV, batteries and a back up generator. This...
Replies
0
Views
190
  • Question
There needs to be a DP means of isolation- if there are other isolators that can be locked that would be OK in my opinion.
Replies
5
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
660
  • Question
Hopefully the N-E fault you have found is enough to explain things, though to trip a 100mA RCD you would need > 50mA and at 400 ohms that is 20V...
Replies
20
Views
4K
  • Question
To clarify this point, connecting an earth rod to a generator does not make it TT. DNO's mains supplies all have an earth electrode at the source...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks