Evening gents just wondered if any of you have come across such a thing when switch is pulled straight down its fine but when pulled at an angle trips power just wondered what your thoughts are
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Pull switch trips Rcd in the UK Electrical Forum area at ElectriciansForums.net
just wondered if any of you have come across such a thing when switch is pulled straight down its fine but when pulled at an angle trips power
I think the clue is in the title. lolWhat do you mean trips power , Trips an MCB , Trips an RCD , what is it that trips ??
I think the clue is in the title. lol
Had this years ago with MK....earth terminal in back box, was mounted to close to switched live. Turn 180 deg and all was ok....Tell tail, was the black arching on the earth terminal block.......worth checking for
OUch, if you are going to be doing fault finding a MFT with RCD ramp test is a must have, unlike a few packets of smokes, or a few nights down the pub, or a few take aways.Cheers will look for it and adjust. Ray galea newish to the game so got basic 1651b tester no Rcd ramp on it unfortunately
Tell me bout it mate wasn't even aware of the ramp test until a few months ago wasn't taught it at college and gutted haven't got it on my tester !!OUch, if you are going to be doing fault finding a MFT with RCD ramp test is a must have, unlike a few packets of smokes, or a few nights down the pub, or a few take aways.