small(.37kw) motor burn't out on a 'pressurization unit'

in a boiler room and burners won't fire


the pressurization unit seems to be an add-on and the pump was fed via 6amp cartridge fuse in boiler panel


just wondering if i should change this to a 'manual motor starter' before replacement arrives

can't read nameplate properly except for 0.37kw and maybe 2. something amps

anyone know right size for this

thanks
 
Problem with very small motors is that it often costs more in protection than the actual motor is worth. I would probably just check the running current, also make sure it isn't short cycling more often than the motor is rated to do (especially with single phase motors) and finally, especially with centrif pumps, use a pressure gauge and check the head pressure (or NPSH) on the system is high enough (some pumps have a minimum head pres requirement to prevent motor overload or an npsh spec to prevent cavitation)
Sorry, I'm in a rush and can't think of anything else.
 
Last edited:

You can’t leave the fuel pump running continuously unless it has a pressure dump valve that returns the fuel to the tank. So a manual starter isn’t really an option. The pump should only run as the burners demand fuel.

Small motors like this tend to have a higher current demand than the O/P would suggest. It’s difficult to estimate the O/L setting.
 
Last edited by a moderator:

You can’t leave the fuel pump running continuously unless it has a pressure dump valve that returns the fuel to the tank.....

I'm not familiar with these particular pumps, I actually imagined it might be a water pump and the burners were interlocked via a water pressure/flow switch. Are they positive displacement?
 
Last edited:
it's a water pump

the 'pressurization unit' is for the water

pump is wired directly via a presssure switch


i'll prob fit thermal overload and check for 'cycling'
 
Last edited by a moderator:
i'll check -as long as windings are protected anyhow


this was added on after to boiler panel and schematic not updated

-i had to physically follow cable from cartridge fuse in trunking to locate problem


when i said the burners won't fire -i meant that the control circuit had been extended out to high and low pressure switches on the 'unit'

i'm assuming this is why burners won't fire -but i'll know soon enough
 
Last edited by a moderator:
If it looks like it was fitted by fly-by-nights I would do all the tests I mentioned above and any others you can think of. It might also be worth checking with the suppliers or on the manufacturers website that the pump they used was suitable for the application in the first place. I would also fit a slow-blow fuse that's rated to the run current plus 10% if possible. That should protect against LRA if something catastrophic happens inside the wet end of the pump.
 
Hey up, davelerave

Are we talking single-phase domestic hot water pumps or 3ph centrifugal?

Regs say motors >0.37kw require overloads (if I recall correctly)...so it's up to you if you want to fit an o/l.

What's the pump manufacture? (Grundfos?)

when i said the burners won't fire -i meant that the control circuit had been extended out to high and low pressure switches on the 'unit'
Are these on unvented boilers for office central heating?
 
Last edited by a moderator:
Hi, how is the pressure/flow regulated on this system? do the pressure switches go through inverters? Only reason i ask is that within certain inverters for instance the ABB acs350 or 550. There is a group for runnning pumps or extraction fans etc. The PID group allows you to set safety limits for over current/torque and also various other faults pumps or motors can come too.

Hope this is of any help

Mike
 

Reply to pump protection in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
It could be that the property has had low mains water pressure problems in the past which may have since been resolved. If you have 2 showers...
Replies
4
Views
4K
  • Question
Sleeving is easier! But some plastic conduit as you did is exactly the same protection against outside metalwork, etc.
Replies
7
Views
3K
  • Question
And here is the said schematic. This is the speed control section, showing the converter, drive motor, magnetic amplifier and related components...
    • Like
    • Informative
Replies
9
Views
2K
  • Question
Fixed that for you Ian!;) Maybe they put the trainees in tech support and as soon as you appear to know something useful you get moved up to a...
Replies
17
Views
4K
Thanks for doing the spade work and forwarding that info. X-rated switches are those that do not have to be derated below their Ith rating for...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks