Hi people

I have been asked to have a look at a house where another firm has put a pump shower 3A and an immersion 3kW on plug tops.

Now having looked at the regs I am of 2 minds... I personally do not like immersions being on plug tops as they don't like being loading for such long periods of time, and I recall being told that fixed appliances of 2kW or more needing to also be on a dedicated supply.

My question is would you have either on plug tops, and whether the immersion should also be on a dedicated supply even if the plug top isn't against the regs.

Regards,

Chris
 
shower pump is OK, but i'd rather see it on a FCU. immersion on a plug is bad practice. it sould be on it's own 16A radial with a 20A D/P switch for isolation/switching.
 
I shared the same opinion Tel, just wanted to make sure I wasn't being pedantic.

Thankyou

I thought I was the pedantic one on this forum, lol, I agree with Tel. However it used to be the norm many moons ago to wire the water heater on the Ring Main as it was called in those days.
 
Agreed,IM should be on it's on circuit, in my old house it was on an plug top off the ring main in airing cupboard, only for back up never got round to sorting it. lol
 
Hi people

I have been asked to have a look at a house where another firm has put a pump shower 3A and an immersion 3kW on plug tops.

Now having looked at the regs I am of 2 minds... I personally do not like immersions being on plug tops as they don't like being loading for such long periods of time, and I recall being told that fixed appliances of 2kW or more needing to also be on a dedicated supply.

My question is would you have either on plug tops, and whether the immersion should also be on a dedicated supply even if the plug top isn't against the regs.

Regards,

Chris

Have they done this as there is only 1 socket in the airing cupboard?
 

Reply to Pump shower, immersion on plug tops in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
899
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
198

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top