• Please use style selector to select BLUE AND WHITE. If you are not already on it. This notice will go once you're on the correct style.

Purpose of testing RCD at 1x and 5x

S

StopTapBob

Can some one please explain why we test at 1 x and then 5 x the rated capatity for a 30Ma RCD? I understand the purpose of the test but I cannot remeber the reason why its 1 and 5 times. Thanks.
 
1 X to see whether it trips at the rated current, 5 x to see if it trips in the required time.
1/2 x to see if the device is too sensitive.
 
I know what the regs states but does anyone know why we test at these ?
It was explained to me at college but I cannot remember it all. I know we test at 30 ma because humans can take up to 30 ma without causing death. Between 60 and 100 ma can prove to be fatal. But why 5x ???
 
I don't know, so this is a guess: we are checking that the RCD is performing as it is expected to according to whichever British Standard it was manufactured to. I haven't seen a copy of BS61008 for example, but I expect there is a time/current curve which specifies the minimum requirements and to ensure compliance more than one test current must be used.
 
It's not to do with that I don't think. I am sure its to do with the effect of shock on the body but I can't remember exactly what the tutor said.
 
It's not to do with that I don't think. I am sure its to do with the effect of shock on the body but I can't remember exactly what the tutor said.



Correct, ...It's all to do with levels of fault current that present itself at the RCD, and the times taken for the RCD device to operate at those higher fault levels...
 
No idea, ...but probably a lot to do with the harmonization with European standards. We state.... 1/2x, 1x, 5x for 30mA RCDs, and the EN state.... 15mA, 30mA, 150mA for 30mA RCDs, ... in there testing regulations.

150mA is when you think about it, a pretty decent test for a 30mA RCD device. There is probably going to be a limit to the speed of tripping an RCD and 0.4 sec is all that is required for other protection devices....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Back