Hi all. So called out to a domestic properety as light fell off ceiling. Put it back together and power all shows good. L/E, L/N power 230v no reading N/E. But no power when connected to fitting? So swapped fitting for 6" pendant and did same? So took the lamp out of pendant and power readings back to normal? Any offers on what is going on? It looks like the lamp is acting as some kind of switch and cutting the power but who knows with out further investigation...
 
bad connection upstream. with no load you are seeing the 230v. as soon as the load tries to pull current, the bad connection fails, dropping the volts. could be either L or N. easieat way to tell is use a voltstick at the fitting with load applied. if it goes out, the fault is on L. if not, it'son N
 
I had a very similar case last week. Customer complained that external PIR was unreliable. Lens was badly clouded so replaced PIR. Set up PIR and everything worked. Called customer to come and see if the was happy with sensitivity and range. Nothing worked. Suspect bulb in fitting so get long ladder out, bulb looks OK. Take PIR off and test voltage, nothing. Check fuses and lights on same circuit all OK. Customer says any connections are under bedroom floor which is sheet, not boards, with carpet on top and there is too much furniture to move. Can I run some T&E around the house to the light?

Still waiting to hear if he want me to run some proper cable around the outside of the house to it.
 
"and then what do you do about the fault under the floor. wait for a fire?"

I have disconnected the live for the PIR at the switch. So I will have to use the cable tracer to see if I can find a jnc box rather than wait for the fire. Assuming he invites me back to sort it properly. He has paid me for fitting the PIR though.
 
as long as the power to the faulty cable/joint/whatever is isolated you can run a new feed external. pref in black flex. it will withstand the weather better than T/E.
 
Digital testers have a time and a place but 99% of the time you don't need millivolt/milliamp accuracy for general electrical fault finding. Most digital tester users don't realise that with a device that has a very very high input resistance you're going to see a lot of voltages that are induced by other cables running in close proximity and the reading on the screen doesn't always mean what they think it does.
 

Reply to Put lamp in holder and the power dies... WHY? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

You too? I thought I was in a unique position:anguished::coldsweat:
    • Like
Replies
5
Views
266
I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top