i have a project at the planning stage at the moment. 100kw across 3ph. dno say that the infrastucture is not capable of feed back, and would need a costly upgrade.

however he says that we can still get the feed back tariff using the pv generated on site but using a controller other than the g59 to prevent feed back to the grid. if anyone could elaborate on this i would be thankful.
 
I guess the DNO are saying you need a system that prevents any export from the site - or at least any export above 16A per phase. You get paid the FiT rate based on what you generate so you don't need to export any. But you would need a load on site that was capable of using all of the 100kW - a dump load (where the power is not usefully used) is not acceptable.

If you export anything at all then the DNO will need to agree the design meets their requirements.
 
thanks for your reply TedM. This was my conversation with our customer. The fact that they may have 100kw on the roof but if they don't have the capability to use it then they are wasting there money, as they will only receive FiT for what they use not what the array is generating. any info on who produces a controller to regulate this?
 
Might be worth investigating hydrogen production for use outwith daylight hours. this may provide a cost effective solution to 24hr power. Solar PV to H2 in storage, the h2 back through a fuel cell to generate power when needed.
 
I think installing 50kW instead of 100kW would do exactly what the SMA power-reducer would do - at a fraction of the cost.

If the power-reducer tells the inverters to throttle back the output then you will not be getting paid FiTs - as nothing/less is being generated.

Looks to me that the practical use of that box outside Germany (where it is mandated) would be very limited unless the legislation changes here.
 
this installation has to be finished before FiT changes!!! no pressure! spoke to dno when they said no, he said that there was a way of using power on site and prevent export to the the grid....... BUT wouldn't tell me how or any contact for information!! very helpfull!! what really puzzles me is the fact that the incoming supply main swith is 800A. the max we would feed back is 144A per phase at peak! i think questions need to be ask as to why the need for an upgrade.
 
Just a thought - the EMMA from CoolPower Products might allow you to divert the excess power into other on-site electrical circuits - but what you put on those circuits which does what you want without it being considered a 'Dump' I'm not sure..
 
Hi solarsystems , was wondering how you got on ?
well! after delay after delay and jumping through hoop after hoop, the DNO allowed us to proceed with our original proposal! no changes and no limits on feed back! we just kept at the and asking to explain the reasons for all limitations until they really couldn't answer why and they turned around and backed down on everything!!! perseverance!
 

Reply to pv generation with no feed back to grid! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
357
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
910
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://www.tlc-direct.co.uk/Products/QUPIR.html?source=adwords&ad_position=&ad_id=&placement=&kw=&network=x&matchtype=&ad_type=pla&product_id=QUPI...
Replies
12
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top