pvc trunking run under loft insulation | on ElectriciansForums

Discuss pvc trunking run under loft insulation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
May 5, 2010
Messages
27
Reaction score
6
was asked this question the other day :-If cables are run in pvc trunking under fibre glass in a loft would the Reference method change ie from B (trunking on a wall) to possibly A (in a thermally insulated wall)?
if not , what reference method would you go for ?
Existing cables in the loft are bunched together and run under fibre glass.
 
If the existing cables are run on top of the ceiling but under fibreglass (presumably insulation) then this would be method 100 or 101. If the cables are then placed in trunking on top of the ceiling and the trunking covered in fibreglass I think this would then be method A.
You would have a similar thermal transfer effect to conduit in an insulated wall. There would be a reduction in heat loss through the insulation so could not be classed as B, but no significant change in heat loss by placing it in trunking rather than directly under insulation, so if the fibreglass is over 100mm then probably best to stick with 101.
 

Reply to pvc trunking run under loft insulation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
563
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top