R

R1CH-G

Just a bit of history first. The following occurred in what is classed as a bunker in the military sense of the word, and all works were carried out to JSP military regs.

Cable used was 2H10 orange sheathed pyro (low smoke zero halides). Cables was potted and glanded and insulation resistance readings taken (500 volts on Fluke 1652) and came back at >500 MegOhms. This cable sat there happily for over 4 months until I got a call saying the DB had gone bang!!

On inspection, the pot was blown to bits! The only thing I can put this down to was dodgy compound and tracking.

Anyone out there who could suggest any alternatives, because for the life of me, I can't work this one out!
 
You wouldn't be the first to experience, what you call ''Dodgy Compound'' lol!!! Can also be old compound that's been on the shelve, past it's sell-by date. The only other thing i can think of in your case is moisture, but i would imagine the length you stripped back for a CU connection, the >500 meg and 4 months in service would justifiably nullify that possibility. ...lol!!!
 
You wouldn't be the first to experience, what you call ''Dodgy Compound'' lol!!! Can also be old compound that's been on the shelve, past it's sell-by date. The only other thing i can think of in your case is moisture, but i would imagine the length you stripped back for a CU connection, the >500 meg and 4 months in service would justifiably nullify that possibility. ...lol!!!

Like I said, it's got me baffled. Only thing I could think of was dodgy compound. I wouldn't imagine that 2H10 pyro exactly flies off the shelves!
 
Joint Services Publications. JSP 375 Vol 3 Chapter 3 Electrical...

But as far as I remember they always stated IAW BS7671 so how the cable was installed badly I don't know?

The cable wasn't installed badly - I know, I installed it!! ;)

Thanks for the heads up on the IAW bit though. I didn't know that.
 

Reply to Pyro Cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top