Got some domestic lighting Pyro with very low insulation reading LN to E 0.07 Megohms.I was thinking of blowing hot air into the termination boxes one at a time while watching the insulation reading.In theory if one varies it might indicate the area of the fault.I have access to the light and switch boxes,but others are under the floor above which is a bit major to lift and all sanded and polished.Anyone else tried this method?(If due to damp of course.)
 
Sounds like a badly designed and installed system to me. If you can't get to the JB's then you're pretty much buggered for doing anything!! Even if you can isolate a section that is causing a problem!!
 
Yes, heat will locate the problem, usually the resistance will fall when you get close to it. You don't need much heat. A soldering iron or lighter flame on a leaky pot will get a response almost immediately. Another possibility is that the cable has been damaged somewhere other than a termination, which you will only tend to discover once you have ruled out the terminations.

As I understand it you can access the joints but with difficulty and cost, so you want to try to narrow it down using only the accessible ends of the cables while they are all interconnected. I had a similar situation where I managed to localise the fault to one box, by resistance heating the cables. Using a low voltage high current transformer I pumped two or three times rated current through the Pyro from each tap-off to the next, while meggering the complete run. By identifying the combination of conductors that triggered a change in insulation when heated, we ended up with only one box under suspicion, which once exposed, revealed a badly made seal where the disc had never seated properly in the pot.

More recently I had an experience with a lighting installation that had so many bad seals that any attempt to localise faults failed miserably, and we had to rewire it completely.
 
Last edited:

Reply to Pyro fault finding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top