Hi all. I am looking for a 3rd opinion on a recently completed install at a friend of a friends property. I am PV installer (17th edition, Part P, 2394&2395, NVQ3), I did not install this system.
- The property has a 3 phase supply.
- The electrician has taken 25mm tails from the main fuses, through a 3 phase generation meter, to a 32A switch fuse... Seems ok so far.
- 6mm 4 core SWA (approx 20M) to the garage from the 32a switch fuse, into a 3 pole rotary isolator... Fine.
- There are two single phase inverters installed in the garage. One is a 5000W Growatt, the other a 3000W Growatt.
Now here's why I am writing this post...
From L2 in the rotary isolator a 2.5mm 3core flex goes to one inverter. And the same from L3 to the other inverter. Nothing from L1.
Thoughts?