I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels everywhere...
Just had my NICEIC assessment which was all fine, and during discussion a few things came up where there seems to be a discrepancy between the BBB and Guidance Note 3 (updated)
The NICEIC's view (and mine now I think) is that for EICRs and CU changes on existing wiring, ALL IR testing can now be done L+N->E at 250V
Only on new installation of cabling does 500V IR need to be done, and that before installing any appliances/accessories that might be affected (USB sockets, switches with LEDs, etc)
GN3 seems to support this with the note:
The second question I clarified was RCD testing - which the NICEIC assessor (and several sources I've seen) was sure can be done once at 1x, on either 'angle' (0 or 180).
GN3 (updated) still says:
BS EN 61557-6 requires the test current for a tripping test to be applied at the zero-crossing point of the AC wave. Therefore, for each of the tests, readings should be taken with the test waveform starting on both positive and negative half-cycles usually identified ‘0°’ and ‘180°’ on test instruments, and the longer operating time recorded for the 1×I∆n Type AC test.
So which is more correct? The BBB doesn't clarify whether one or two tests at 1x is acceptable....
Finally, the latest triumph in the PRS legislation's many flaws.
As currently enacted, it states clearly:
“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);
Which would suggest that until they bother to pass a new law to change it, EICRs for the purpose of PRS MUST be done to 18th Amendment 1 (even if that happens to be after September when AMD 1 is withdrawn??)
Of course a competent legislator would have got round that by saying 'regulations currently in force', or some such legalese, to avoid more work for bill drafters....
Any one else ---- enough to give a ---- about such things and willing to offer their views?
Just had my NICEIC assessment which was all fine, and during discussion a few things came up where there seems to be a discrepancy between the BBB and Guidance Note 3 (updated)
The NICEIC's view (and mine now I think) is that for EICRs and CU changes on existing wiring, ALL IR testing can now be done L+N->E at 250V
Only on new installation of cabling does 500V IR need to be done, and that before installing any appliances/accessories that might be affected (USB sockets, switches with LEDs, etc)
GN3 seems to support this with the note:
BS 7671:2018+A2:2022 permits the test voltage applied to circuits following connection of equipment to be reduced to 250 V DC, provided that cables were tested at 500 V DC prior to connection.
Although it then goes on to say minimum values of 500V as normal - and add that simple installations with no distribution circuits should preferably be tested as a whole.
Although it then goes on to say minimum values of 500V as normal - and add that simple installations with no distribution circuits should preferably be tested as a whole.
The second question I clarified was RCD testing - which the NICEIC assessor (and several sources I've seen) was sure can be done once at 1x, on either 'angle' (0 or 180).
GN3 (updated) still says:
BS EN 61557-6 requires the test current for a tripping test to be applied at the zero-crossing point of the AC wave. Therefore, for each of the tests, readings should be taken with the test waveform starting on both positive and negative half-cycles usually identified ‘0°’ and ‘180°’ on test instruments, and the longer operating time recorded for the 1×I∆n Type AC test.
So which is more correct? The BBB doesn't clarify whether one or two tests at 1x is acceptable....
Finally, the latest triumph in the PRS legislation's many flaws.
As currently enacted, it states clearly:
“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);
Which would suggest that until they bother to pass a new law to change it, EICRs for the purpose of PRS MUST be done to 18th Amendment 1 (even if that happens to be after September when AMD 1 is withdrawn??)
Of course a competent legislator would have got round that by saying 'regulations currently in force', or some such legalese, to avoid more work for bill drafters....
Any one else ---- enough to give a ---- about such things and willing to offer their views?