Hi i have a 50 m run from the dno intake in the garage to the house. I have decided to run a 3 core armoured and install a switch fuse at the garage end. The only trouble is though a 35mm armoured is a bitch to terminate in a single phase board. Anyone come across this problem just wandering as i did a 25mm earth in a single phase board and that only just fit. Thanks in advance
 
make off the armour in a Spreader box mounted tight to your switch fuse having removed the gland plate from the bottom with 35mm you could use an off cut of 6inch steel trunking with a slot cut and some Plexion between and cut slightly smaller than the slot
 
then out of the spreader box what size would i bring out?? as i thought you had to use the same csa all the way throughout and its the the termination into the earth bar that i am going to have the most trouble with and into the main switch. Thanks for your advice i really appreciate it
 
strip the armour and gland as per normal(bw or Cw) leave the tails long enough to go straight to the switch fuse and a 25mm flying bond from the banjo/fryingpan to the switch fuse If its an ME Exel type theres a nut n bolt you could put a crimp on
 

Reply to query in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
137
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
928
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

And if it's a garage then use metal clad accessories.
Replies
5
Views
483
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
287

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top