The previous owner has removed the shower and taken it with them before moving out and has left the 10mm Red+Black t&e sticking out of the wall.

Question 1:- What do we do from this point and why?

1:- Basically we need to make sure that this cable is not live and is safe to work on. Lets think about the circuit itself:- It draws power from the C/U, local isolation from a pullcord/switch and feeds a shower unit. See if the local isolation switch is on or off (if it shows you without power). Go to the C/U and see if there is a circuit marked up as downstairs shower or any 40A mcb’s. If you cant locate the mcb, ask permission to turn off the main Isolation DP switch at the C/U for the house, lock off and hang notice.
With an “approved Voltage indicator or test lamp” as recommended in HSE Guidance Note GS38. The test instrument should be proved to be working on a known live source or proving unit before and after use. With caution test L-N, L-E and N-E of the bare ends of wire from the cable. Should be dead but you never know. Now place each wire in a 60A terminal block ensuring a good safe connection, better than leaving bare cables hanging around and we will need it later.
In this case the redundant 10mm t&e has been disconnected from the C/U and just place on the floor underneath the C/U with a note on it "Not in use". Very nice of the person that disconnected it but at the end of the day, we are electricians, WE DONT GUESS, WE TEST.
At the C/U end, same as above, test these ends. All show dead, this is looking to be the other end of the cable but we need to confirm that.
With a single 60A terminal block (just for the size really) connect L-E at the C/U end. Go to the shower room and place test probes on L+E terminations block to test for continuity using a “low resistance Ohm meter”. If you get a reading great! You have found the cable but we need to confirm this so disconnect and test again, should get open line.

If you don’t get a reading on the first continuity test, take off your probes, switch on at the local isolation pullcord switch and test for dead again before doing anything else, it could be fed from another source and at this moment in time we do not know????

OK we have found the start and end of the mystery shower cable, well done. If this shower room was no longer going to be in use/changed to another function or a shower was not going to be put back in we need to terminate the ends (already done) and put into the correct type of enclosure for the room/environment at both ends.
 
Question 2:- How do we go about installing a new shower unit?


2:- We need to establish if this cable is still fit for use before installing the new shower. How we do that is by testing of course. Just like doing the dead tests on a new install, we carry out the same procedure but with the addition of a visual inspection of the cable we can see and estimate the cable route. On your Minor Works Certificate we need to report that we did not install the cable (it would be an EIC if we did btw) and we can not see the cable route.

I don’t want to go into the testing procedures, that is for another thread but if you follow the sequence of tests and the reasons behind them you will have a head start on a forthcoming thread.
 
I'm going to look through all the answers again tomorrow night but I will say this today.

Only two people would ask the home owner permission before isolating power to the house (very good point and btw it is a C&G exam question).

I'll post up some feed back from your PM's tomorrow after work (yes on a Sunday lol). Taking the night off and putting my feet up and watching a movie. I've had enough electrics for one week lol.
 

Reply to Question #2 Shower Answers in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
922
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top