Job is to extend a kitchen ring circuit, and have a question about Insulation Resistance values.
Tests on existing ring (2.5/1.5 t&e) carried out and results as follows -
Ring continuity (end to end)
R1-R1 = .38W
RN-RN = .42W
R2-R2 = .64W
Continuity W
R1-R2 = .34W
Insulation Resistance MW
R1-R2 = 30.4 MW
R1-RN = >299 MW
RN-R2 = >299 MW
I have inspected and checked for tightness all (except one difficult to get to socket) terminations at each accessory.
I know that above 2MW is considered acceptable, but what could be the cause of this R1-R2 value of 30.4MW? when each conductor tested in a different configuration (R1-RN & RN-R2) reaches >299MW ?
Any clues/ideas would be greatly appreciated, many thanks.