Hi, the maximum demand (load) in a property is as follows:

(4x32+4x6)0.40 = 60.8 amps and the main fuse rating is 60 amps.

Does this comply, taking tolerance into consideration? What is the tolerance in this kind of situation? Should I ask DNO to upgrade the fuse and the tails? Many thanks!
 
You've multiplied the whole installation by 40%? Why is that?
4x6? Does that mean 4 x Light circuits? Do you know the individual circuit demand?
 
The formula is actually 100% current demand of largest circuit + 40% current demand of every other circuit.

In your case it would be..

32A
(Largest circuit) + (3 x 32 x 0.4 = 38.4A) + (4 x 6 x 0.4 = 9.6A)

32 + 38.4 + 9.6 = 80A
 
examples:

6amp lighting circuit -66% of total current demand
i=p/v
6 lamps at 100w=600w
600w/230=2.6amps
2.6amps = 100% 2.6/100 = 0.026= 1% 0.026x66
= 1.71 amps

20 amp genaral socket = no diversity
=20 amps

32amp rfc= 100% of largest point of utilisation and then 40% of current demand on any additional rfc
=32 amps

40 amp cooker = take 10 amps away and then 30% of whats left +10 amps
40-10 =30
30x0.3=9
10=9=19amps

maximum demand=
1.71a+20a+32a+19a= 72.71amps
 
Maximum demand calculations are bit of a gray area, the formulas outlined above are recognised and found in the IEE books but also note that "The use of other methods of determining maximum demand is not precluded where specified by a competent person" (Guidance Note 1, Selection and Erection). If you (as a competent person, well versed in the aspects of maximum demand and know what kind of maximum current can be used at any one time) can calculate and alternative method with good reasons then the figure you come out with can also be used. Usually your proof of competency is the old 2400 which is now 2391-2. If anyone has anything to add or correct me I'll be happy to hear them out. Cheers.
 
32amp rfc= 100% of largest point of utilisation and then 40% of current demand on any additional rfc
=32 amps

Not quite right.

Socket outlets -- 100% current demand of largest point of utilisation and then 40% current demand of every other point of utilisation

Largest point of utilisation being 13A and then 5.2A (13 x 0.4) for every other point of utilisation.
 
Maximum demand calculations are bit of a gray area, the formulas outlined above are recognised and found in the IEE books but also note that "The use of other methods of determining maximum demand is not precluded where specified by a competent person" (Guidance Note 1, Selection and Erection). If you (as a competent person, well versed in the aspects of maximum demand and know what kind of maximum current can be used at any one time) can calculate and alternative method with good reasons then the figure you come out with can also be used. Usually your proof of competency is the old 2400 which is now 2391-2. If anyone has anything to add or correct me I'll be happy to hear them out. Cheers.

I agree with the other methods of determining maximum demand but don't look upon proof of competency as being one particular qualification-it's a combination of qualifications and experience.

In this case, if it's an existing installation, a better assessment of maximum demand could be made just by talking to the client regarding use of the installation.
 
Ive done the 2392 course and we were told to simply add up each breaker and that number is the maxium demand for the installation, if its an 3phase board you record the highest one. We were shown this in the regs but i cant find it.
 
Ive done the 2392 course and we were told to simply add up each breaker and that number is the maxium demand for the installation, if its an 3phase board you record the highest one. We were shown this in the regs but i cant find it.
if you did that, there'd be thousands of houses wanting 200A supplies.
 

Reply to Question on maximum demand (load) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
510
  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top