Scott89

Supply two rings, 2 lighting circuits, 1 heating circuit with 2 x 2kw heaters
Outbuilding is 60 meters away from supply. Was thinking 25mill to cover me but advice would be nice?
 
Supply two rings, 2 lighting circuits, 1 heating circuit with 2 x 2kw heaters
Outbuilding is 60 meters away from supply. Was thinking 25mill to cover me but advice would be nice?

2 lighting circuits- what kinda lights, how many, total load?
Two rings- to power what, max load?

help us to help you!
 
we have just done a similar job, the customer had his own cable...35mm 3 core aluminium. that was nice to work with lol but it was plenty big enough
 
if you calculate volt drop 16mm would give you 32 amp max so would go with 25mm 3 core swa will give you anything from 40 to 60 amp supply to allow for future additions
 
do it in 95mm and future proof it for ever more!

Personally i would do 240mm just to be sure:D

Idiots! And you call yourself sparks! Yeeeehaaa! I bet you rip off all your customers like this don't'cha, trying to sell them bigger, more expensive cables than neccessary! 1mm T+E will more than suffice! :D
 
Thanks for a the comments. It's just a double garage conversion for small office and toilet. 8 double sockets inside. 2 double sockets outside. 4 x standard 600 by 600 fluorescent lights. 3 x outside pit floods and 2 x 2 kw heaters
 

Reply to Question on supply size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...
Replies
7
Views
496
Agreed, i have a cabin in the woods, water heating and hob is via 19Kg propane bottles, lasts ages and space heating is via warm air heaters via...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top