nazoom

Hi

I am trying to fill in Section (K) of Electrical Installation Condition Report. My question is when we have faults like: High Insulation resistance on a certain circuit that i know, High resistance of main bonding that i identified, Zs too high for ring, ring discontinuous and incorrect polarity for light circuits that i inspected. What do i put in the (Furhter Investigation Required) section? For these faults do i put No or Yes?

Many Thanks
 
You will have listed faults and defects in section F. In the tick box section of items inspected if a code is attributed to a particular item I refer it to section F. ie....'Section F item 3'.
The FI box would only be used if you were unable to reach a conclusion about an item and further investigation is required...again this could be referred to section F. In practice the FI box is almost never used as in most cases if you have coded an item no FI is needed,just rectification.
 

Reply to Question regarding filling Section K of Electrical Installation Condition Report. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
856
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top