Industrial installation (non-domestic). Here's the scenario:
A large (150kW) 3-phase motor circuit where the supply is taken from a starter fitted with 315A BS88 HRC fuses.
From calculation using the cable data, the Zs value exceeds the manufacturers requirement for 5s disconnection time (similar to table 41.4 of the 17th Edition).
An additional earth cable has been installed to a main earth tape located near the motor end to achieve supplementary bonding.
My questions are: 1). How can this addition of supplementary bonding prove compliance with the regs? and 2). What use is an earth loop impedance test taken at the starter?
Any comments gratefully received.
Thanks in advance. Steveb555