enginearin
Hello all,
I am undertaking electrical installation in a new build house myself (notified to building control and will be inspected by them for sign off) and i am looking for some advice on providing power to a kitchen island.
I had installed two cable ducts within the floor slab to carry the feed to induction hob and to carry the ring circuit or fused spur onto the island for a couple of sockets. Unfortunately the wife has changed the kitchen design since and this has left me with only one available duct. To further compound the issues, the single four ring hob has now become two two ring hobs (max 16A each, 1.5mm flex cables attached).
In light of these issues i was considering running a single supply to the island (RCD protected with 40A MCB in the CU) then fitting a small CU with individual 16A MCBs for the hobs and say 6A MCB for a radial with a couple of sockets. The question i have, is whether it is acceptable to run this feed to the island in Twin and Earth (provided it meets the current carrying criteria when derating factors are applied)? It will be deeper than 50mm in the ceiling / false wall until it becomes clipped direct (on wall surface) behind kitchen units to enter the duct so i believe this (in combination with the RCD) means that armoured cable is not required.
Obviously cable CSA are getting large here... Would it be prudent to apply any level of diversity when considering cable derating factors (i cant see all four rings on the hobs going full chat continuously at the same time)
Any comments / pointers / previous experience greatly appreciated
Thanks
Tim
I am undertaking electrical installation in a new build house myself (notified to building control and will be inspected by them for sign off) and i am looking for some advice on providing power to a kitchen island.
I had installed two cable ducts within the floor slab to carry the feed to induction hob and to carry the ring circuit or fused spur onto the island for a couple of sockets. Unfortunately the wife has changed the kitchen design since and this has left me with only one available duct. To further compound the issues, the single four ring hob has now become two two ring hobs (max 16A each, 1.5mm flex cables attached).
In light of these issues i was considering running a single supply to the island (RCD protected with 40A MCB in the CU) then fitting a small CU with individual 16A MCBs for the hobs and say 6A MCB for a radial with a couple of sockets. The question i have, is whether it is acceptable to run this feed to the island in Twin and Earth (provided it meets the current carrying criteria when derating factors are applied)? It will be deeper than 50mm in the ceiling / false wall until it becomes clipped direct (on wall surface) behind kitchen units to enter the duct so i believe this (in combination with the RCD) means that armoured cable is not required.
Obviously cable CSA are getting large here... Would it be prudent to apply any level of diversity when considering cable derating factors (i cant see all four rings on the hobs going full chat continuously at the same time)
Any comments / pointers / previous experience greatly appreciated
Thanks
Tim