3 phase heater no neutral. in the fuse board itsd been wired up as 2 phases and neutral , why does it work ??????:thinking:
 
various explanations - what kind of heater is it?
 
so in other words, one of the coils has been wired to the neutral, and the other 2, each have a phase to them?

if so, then the heater will still work, as you have effectively shared a neutral between 2 single phase loads, albeit through a higher impedance.


any 3ph 4wire system uses this principle, as the max current that can flow in the neutral is equal to one phase. (harmonics muddy the water slighlty)
 
Some ppl think the blue/black has to go to netural :D

Most likely explanation!

But surely the type of heater has to be relevant, too? I'm making an assumption its a big blower with a 3ph fan motor inside - if it's a diddly little halogen or IR then the 'balanced' theory starts to fall apart.
 
hmmm i changed it back to 3 phase i'll have to ring up the company and see if its blowing out more heat ??
Based on what you have described, I would agree that Matmoo has probably the most likely explanation. However, it may be wise to fully understand what's really going on before re-connecting the 3rd phase, particularly if its an old unit. For instance, someone may have replaced 400v control gear with 230v or the elements themselves may have been changed for 230v.
 
You say, it's 3 phase, but is it?
A lot of 3 phase heaters, have single phase elements, each being supplied by just one of the phases.
Obviously they then require a neutral.
How many elements are there, is there any single phase control gear?
Sometimes with 3 phase machines, there is a transformer, and neutral connections are connected to the star point of the transformer.
I've also seen some machines (mostly eastern European, where they have a 5 pin plug, TPN&E, yet inside the machine, the N & E are connected together.
 

Reply to question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

A week later, and another update. I had been looking at the app settings at home, and reading the MI, it seems the problem.... since last week...
Replies
13
Views
1K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top