..then you've narrowed it down to 1 circuit...
,or could you clamp the cpc to see if any current is flowing...although im not sure if this would be possible as it would of tripped..
All the loads (appliances) were unplugged and if the tripping fault occurs when a combination of circuits are powered up I'm afraid it's unlikely to be a N-E short. You're spot on with the visual inspection technique but it's always nice to focus your search to the largest leakage faults first and not to waste time chasing the very small faults that normally wouldn't be a problem.Need to visually inspect every load to make sure a live/neutral isn't touching anything e.g back box, and nothing is going down to earth
could you use a clamp meter,to either clamp the live and then the neutral to check the current is equal,and none is flowing to earth as this would cause the rcd to operate,or could you clamp the cpc to see if any current is flowing...although im not sure if this would be possible as it would of tripped..