Hi all,
just joined so first post.
Triton say their electric showers must be RCD protected. I was under the impression that manufacturers recommendations superseded electrical body's regulations but according to Elecsa's technical dept that is no longer the case. I was told that in the 18th edition the clause states that you must be aware of manufacturers recommendations. Am i missing something here or is this a step backwards.
 
Last edited by a moderator:
regs. state that MFI should be taken into account, i.e. sometimes they are wrong. in any case, BS7671 states that all circuits ib a special location ( bath/shower room ) must be RCD protected. in this case BS7671 anf MFI instructions are in harmony.both singing the same song.
 
Last edited by a moderator:
as i understand it, MFI should be followed if they comply with BS7671. . if not, they should be considered. then again, I'm old school. if it can't be sorted, hit it with a hammer.
 
Hi all,
just joined so first post.
Triton say their electric showers must be RCD protected. I was under the impression that manufacturers recommendations superseded electrical body's regulations but according to Elecsa's technical dept that is no longer the case. I was told that in the 18th edition the clause states that you must be aware of manufacturers recommendations. Am i missing something here or is this a step backwards.
In general, manufacturers’ Instructions are to be taken into account.
However there are certain areas where the requirements are to comply with the Manufacturers’ Instructions.
Off the top of my head, any Type tested DB, some lighting installations and some medical equipment.
 
I would not want to install an electric shower without RCD protection, however if you tell the customer that it has to be installed with an RCd as per MFI and he/she is a smart arse and pulls some reg out of the air, you can look as though you're trying to stitch them over. It is a like for like replacement but even so as a professional fitting an RCD should be a matter of course.
 
Its all well taking manufacturers instructions into account,that is as long as a linguist with expertise in English words for Chinese and Japanese infant school interpretations is on hand

He would need to explain exactly or even in most cases give some idea of what information it is they intend to impart to the unlucky spark who initially reads the garbage
 
MF instructions are sometimes bizarre to say the least, I connected an oven for a family member the other day and the instructions said that this appliance must be or maybe was should be connected with a 45 amp fuse as the ocpd.
Does this mean that I can’t use an mcb rated at 32 or 40 amps as the ocpd? This is where I ignore them ha
 
Hypothetical.

You’re asked to change a shower as old on is busted. OCPD is an mcb, no rcd. Like for like replacement? Do you fit an rcd to that circuit as per regs?

You’re asked to change a ceiling pendant. Old one is busted. OCPD is an mcb, no rcd. Like for like replacement? Do you fit an rcd as per regs?

I was going to use the “change a lightbulb” example, but the thread would just go into a bulb v lamp discussion, and we’ve covered that elsewhere a number of times.
 

Reply to questioning rcd re shower installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have just completed the 'Wallbox' on line courses. Seems to me that you need to install extra equipment (a Power meter) in the consumer unit to...
    • Like
2
Replies
18
Views
2K
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top